under the 17th sockets can be omitted from an RCD by means of machanical protection i.e steel conduit. But if this socket can be used to supply equipment used outside the equipotential zone i.e lawn mower does this need to have an RCD?
but surely with an extension lead all sockets could be used. And if a socket is specifically labeled for a piece of equipment the cables would have to be 50mm deep or mechanically protected still. Think thats where ive got my wires crossed
411.3.3 Additional protection
In a.c. systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket-outlets with a rated current not exceeding 20A that are for use by ordinary persons and are intended for general use, and
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted for:
(a) socket-outlets for use under the supervision of skilled or instructed persons, e.g. in some commercial or industrial locations, or
(b) a specific labeled or otherwise suitably identified socket-outlet provided for connection of a particular item of equipment.
Care to tell us which regulation says that?under the 17th sockets can be omitted from an RCD by means of machanical protection i.e steel conduit.
Aye, or you may even use a different type of socket to the norm such as a round pin one.
er... the one i listed above..
The regulation you quoted says nothing about sockets not needing RCD protection by reason of mechanical protection...under the 17th sockets can be omitted from an RCD by means of machanical protection i.e steel conduit.
but surely with an extension lead all sockets could be used.