With regard to the design of circuits, you basically need to consider a few things.
1) For a kitchen you will typically have a 32amp supply for the Cooker, which is dedicated to the cooker and cannot have any sockets connected to it. i.e. the UK style cooker control unit isn't permitted, we just use a double pole switch near-by.
2) For an average kitchen, two radials will be quite sufficient for the sockets, however, you need to consider how many appliances you have. For example, if you have a washer and dryer in the kitchen, it's normal practice that they'd have their own dedicated radial circuit, so you would need to consider installing a 3rd radial.
Again, it entirely depends on what you're installing.
Basically, washing machines / dishwasher and dryers don't actually draw that much of an inductive load, i.e. the motor, the peak will come when the machine is heating. Most of these appliances contain a large heater, up to 2.2kW.
Calculate the load by reading the information plate on the appliance, it will give you a rating in watts. Divide this number by 230 volts and you'll get the peak ampage drawn.
Then just make sure that you've enough circuits to provide power to allow you to run all those machines simultaneously.
Usually, a washer and dryer will not draw more than 20A. However, you'd really be pushing it if you try to install a washer, dryer and dishwasher on a single radial.
Also, when you're installing the sockets in the kitchen, make sure that you don't accidentally put all three e heavy appliances on the same circuit!
3) Also, under the new regs, if you're installing a freezer, to prevent spoilage of food, you can opt to run a single socket fed from a 16A MCBO. This will not trip with the rest of the sockets in the event of an RCD trip.
Basically, consider how many major appliances you're installing!
For normal domestic sockets, outside of the kitchen, you typically use a single radial for a large room with lots of sockets e.g. your living room / dining room etc, ( often this will feed one or two sockets in a near-by hall area too, you do not need to consider a hall as a separate room, unless you're planning to run serious amounts of plug-in heating or something..))
Bedrooms / less heavily used rooms typically share 1 radial for two rooms. This is the maximum number of rooms that a radial can serve.
Increasingly, it's common to install a dedicated 20 amp radial on a MCBO (Combined breaker / RCD device) to feed your office / study area, this prevents IT disasters in the event of a wet iron / kettle tripping the RCD. It really only becomes an issue if you've got a home office, or are really fussy about your IT equipment.
Our RCD has only tripped about once in 5 years, and that was due to a wet iron. So, in general it's not really a big problem and when it does trip it usually indicates that something's seriously faulty i.e. wet iron, leaky washing machine, leaky dishwasher etc will usually be the culprit!
Irish distribution panels differ quite substantially from their UK counterparts.
First of all, there's a master breaker / main fuse on the panel. This is designed to trip/blow in the event of the panel being overloaded. In the UK and in most other countries, they rely on the service fuse for this.
Secondly, we use 10A radials for lighting, with a maximum of 10 points per radial.
You will typically see 6, 8 or 10 radials X 20A radials feeding sockets, usually labeled for each room / each group of rooms being served.
If you find this confusing, it's really advisable to contact a qualified, registered electrician.
Because of the serious fall-off in house building in Ireland due to the property crash, there are loads of sparks out there who will consider any job, no matter how small and they're also much better value than they used to be.
You can get a list, by contacting RECI (www.reci.ie) (Register of Electrical Contractors of Ireland)
Or, if you're stuck, try
www.bidjob.ie or
www.tenderme.ie, both sites let you put up your job specs, and trades people will tender for them.
Serious modifications to a wiring system really should only be undertaken by an electrician. If you're going beyond installing a couple of extra sockets, I would strongly suggest getting someone professional in.
For major work you will require a completion certificate, and your insurance company can come looking for this in the event of a house fire. So be very careful!