Agile said:
The meter regulator should be checked for correct operation. That means less than 1 mB reduction in output pressure between min and max power.
Anyone installing a pre-mix boiler without the facilities to test for CO² is not equipped to do the job properly.
Tony
The correct pressure at the meter on part load should be around 21 mB. Its irrelevant what it is with no load ! On full load it should still be at 20 mB as I explained before. The Gas Transporter will replace the meter regulator free ( 0800 111999 ) if requested.
Whilst you say the pressure at the meter is only 19 mB at full load but you dont quote this at the boiler. If its more than 1 mB pressure loss as demanded by the regulations then the boiler can be difficult to set up correctly.
If its the normal foghorn sound then its only produced at minimum power. Thats on startup or when the heating modulates back after ( in your case ) about 10-15 minutes.
Its caused be a weak mixture and usually measures less that 8.7 % CO².
The average three bed semi has a heat loss of 10-12 kW. Unless you have a six bedroom detached house with poor insulation your boilers is set way too high for CH at 21 kW. The only loser is you as the efficiency falls due to less operation at a higher condensation and a slightly less constant room temperature.
Its difficult to guess whats the main problem from the info you have given. You say "it was set correctly last October". One assumes this is by your installer but you also say your local installers dont have FGAs? Why are you apparently unable to call him back to check it again?
The thermal cycling and the ageing of components like the meter regulator will cause the exact operating conditions to vary slightly with time and this is one reason why boilers need servicing anually and resetting to the optimum manufacturer's operating parameters.
However, the above relates to the normal situation of the noise at minimum power! Yours as you have written it is only on higher power! That would imply a flue fault perhaps a failing flue seal allowing combustion gasses to recirculate. Thats assuming the inlet gas pressure is correct !
Tony Glazier