Carrying out some PIRs to some challets on a Holiday Park - The onsite handyman has recently swapped the old wylex rewireable boards for some new consumer units...

1302368785.jpg
 
Sponsored Links
Reverse polarity on the incomming...

...It even has a sticker to help :LOL:
 
Polarity to isolator wrong way round so the busbar will be nuetral, and polarity wrong everywhere. Nice!
 
Sponsored Links
Obviously no testing of any sort was done.
The two MCBs - they might not be a failure (but probably are given it is a holiday chalet) but why not have all RCBOs in such a small unit? Would only be another £40 or so.

Then again if the owners have their 'handyman' replacing consumer units they clearly have no concern for the safety of their customers or anyone else. They should be reported to the local authority and hopefully prosecuted.
 