No, there are double insulated, no earth required, but normally connected for continuity.Been working past 7 years so I guess it’s not an issue.

No, there are double insulated, no earth required, but normally connected for continuity.Been working past 7 years so I guess it’s not an issue.
No, there are double insulated, no earth required, but normally connected for continuity.

Where did you get that from?The cpc must be connected or else you won’t have continuity of the CPC back to the CU
BS 7671:Where did you get that from?

Well, yes, but is that the same thing? It is terminated at the accessory, and given the rest aren't connected because there is no earth connection, what's the point? And also that BS 7671 isn't the law, I just was questioning where the "must" came from?BS 7671:
"A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point".
Where did you get that from?

There in no "must" though. Yes, common sense, better for testing etc. etc., but no more than that.Understanding BS 7671
It sounds as though you were enjoying the Garage Lighting thread so much, all 8 pages of it, that you want to start it again. I'm already bored with the topic, so won't be taking part.Well, yes, but is that the same thing?
There is if you want to, or have to, follow BS7671. Like electricians do.There in no "must" though.

The OP isn't an electrician, he/she is a DIYer who came for a bit of advice. Connect one downlight like before or get an electrician in. That's it really.There is if you want to, or have to, follow BS7671. Like electricians do.

Well, yes, but is that the same thing? It is terminated at the accessory, and given the rest aren't connected because there is no earth connection, what's the point?
And also that BS 7671 isn't the law, I just was questioning where the "must" came from?
The cpc must be connected or else you won’t have continuity of the CPC back to the CU

The OP isn't an electrician, he/she is a DIYer who came for a bit of advice.

I don't know why people chop off the earth, yes the lights are a crap design