Well indeed!In fact, if he had wanted to split hairs, he could have gone a bit further. Even with present day CUs, there is a short 'single' path between the MCB and the ...
Well indeed!In fact, if he had wanted to split hairs, he could have gone a bit further. Even with present day CUs, there is a short 'single' path between the MCB and the ...
It was PROBABLY removed shortly after common sense itself became such a rarity.I wish the wiring regulations still said common sense should prevail but that has gone.
I can't see that it could be said to offer any (electrical) advantages over a conventional ring or radial final circuit (and haven't seen anyone claiming that), but nor do I see that it presents any electrical disadvantages in comparison with a conventional ring final circuit - as has been pointed out, the only difference is the length of the 'common' conductors from the OPD mechanism before it splits into the two arms of the ring.Given the number of times we see quotes along the lines of "If we were starting now, ring final circuits would never be allowed", I don't see why we would expect to see the lollipop circuit adopted. What advantages would this give over ring or radial circuits?
On rings having two equally long "tails" at the ends which make up a significant proportion of the total length is a good thing because it improves balance. If all the load on a ring is in the center third and the capacity of the ring cables is at least two thirds of the breaker rating then it is not possible to overload the cable without overloading the circuit as a whole.but nor do I see that it presents any electrical disadvantages in comparison with a conventional ring final circuit
Yes, that's technically true, but ...On rings having two equally long "tails" at the ends which make up a significant proportion of the total length is a good thing because it improves balance. If all the load on a ring is in the center third and the capacity of the ring cables is at least two thirds of the breaker rating then it is not possible to overload the cable without overloading the circuit as a whole.but nor do I see that it presents any electrical disadvantages in comparison with a conventional ring final circuit
... so is that (true).Having said that a lollipop circuit is no worse in this regard than a ring that happens to serve loads close to the DB.
I don't see why the term final (or is it Ring Final Circuit) should make you cringe Eric.
I don't see why the term final (or is it Ring Final Circuit) should make you cringe Eric.
Where FCU are used on a ring circuit it's not the final circuit as by definition a circuit is all protected by a automatic disconnection device so since a FCU will automatically disconnect the wiring after the FCU could well be regraded as a circuit so clearly the ring is not the final circuit in that case.
As to ring v radial I would agree there are problems with the ring but in the main down to poor maintenance rather than something wrong with system.
It would presumably have to be 'very near', since 'at the CU' would be a ring, not a lollipop (unless one is splitting hairs about the internal components of an OPD, and the single cable supplying the neutral bar - in which case all rings are technically lollipops!),Hi John, I was querying the point in reworking the ring circuit to lollipop at (or very near) the CU.
Interesting question. Without thinking too deeply, I imagine that the 'continuity' tests would have to be undertaken from the point of origin of the lollipop's 'ring', and everything else would be as for a standard ring - but I'd need to think more carefully before being sure about that.I'm not sure what tests would need to be carried out on a lollipop for an EIC.
Sounds about like what I would expect. Im planning to make the juntion in question accessable for said same.Interesting question. Without thinking too deeply, I imagine that the 'continuity' tests would have to be undertaken from the point of origin of the lollipop's 'ring', and everything else would be as for a standard ring - but I'd need to think more carefully before being sure about that.I'm not sure what tests would need to be carried out on a lollipop for an EIC.
This, of course, is where one of the potential problems arises. Since it's not conventional (and hence probably 'not in their I&T book') some 'electricians' might be thrown by a lollipop circuit - and either just not know what to do or, perhaps more likely, just test the circuit as if it were a radial. At the least, I think some clear labelling/documentation in the vicinity of the CU would be in order. Without such prompts, even a clued-up electrician might not suspect that a circuit leaving the CU in a single cable was a lollipop (although the size of the cable ought to give a clue that something 'unusual' was going on).Sounds about like what I would expect. Im planning to make the juntion in question accessable for said same.Interesting question. Without thinking too deeply, I imagine that the 'continuity' tests would have to be undertaken from the point of origin of the lollipop's 'ring', and everything else would be as for a standard ring - but I'd need to think more carefully before being sure about that.I'm not sure what tests would need to be carried out on a lollipop for an EIC.
Indeed. The house currently has an ECIR, but the 6mm spur had been taken out of the CU and connected behind the board with choco block into two short lenghts of 2.5mm and thus disgused, and oddly, passed the continunity tests with ease...This, of course, is where one of the potential problems arises. Since it's not conventional and hence probably 'not in their I&T book'....