Runners should be ok, but if they have those little plastic wheels, glue some wahsers on them. You should be sorted then
That's why I keep asking you what you mean by "exposed". You don't bond conductive parts which are not earthed....
Thank you for your opinion.As you beg so nicely for enlightment I will enlighten you as to me opinion.
That's a definition with no relevance to the definitions of either exposed-conductive-parts or extraneous-conductive-parts, or the regulations for either main or supplementary equipotential bonding.Exposed metal is to me any metal which can be touched ( including any that is behind removable covers ) and may become electrically live as a result of one or two faults happening.
Should be?Metal legs of a metal topped desk on which electrical equipment may be used could become live along with the top and should be bonded.
That's not bonding, it's earthing.Some laboratory and other work places insist on such desks being bonded to earth.
And I've seen helmetless people riding motorcycles whilst wearing shorts, t-shirts and flip-flops.I have seen the vertical columns of metal shelf support systems bonded to earth where metal shelfs could be fitted and electrical items used on the shelves.
Is such a desk an extraneous-conductive-part?
Oh - and BTW - that's earthing again, not bonding.
bernardgreen";p="1296335 said:Metal legs of a metal topped desk on which electrical equipment may be used could become live along with the top and should be bonded. Some laboratory and other work places insist on such desks being bonded to earth.
Are you sure this isn't to prevent against static damage to electronic components ?
If that was the evaluation of the equipment it should have been put in the skip.
And what if the metal they are touching is only bonded, and therefore live, because you've been along and connected it to the electrical system when it should not have been because it was not an extraneous-conductive-part?And how do you see the the regulations on bonding that is not earthing coping with the "through the window" scenario and make it safe.
This where someone inside a room hands an item to a person outside in the garden. The person in the garden is on the ground, effectively earthed. The person inside the room is touching a bonded item of metal. The bond is as per regulations connecting that piece of metal to the case of a faulty piece of equipment which due to the fault has a case that is live.
Can't it?Now to me it seems clear that if "bonding" is always to the true earth directly or in-directly then the "through the window shock" cannot happen.
And what does connecting something which had nothing to do with the electrical installation, or earth, to the electrical installation do?It just seems that bonding that is not an earth bond simple extends the shock hazard from a faulty item on to all other items that are bonded.
If they were so unsure of the quality of their design or manufacturing that they thought there was a risk that within the first hour of the equipment's life it would fail so catastrophically that the case would become live then they should have changed the design or the way they made it.The equipment was being soak tested immediately after manufacturer and prior to being packaged and sent on to be sold. 99% of failures would occur in the first hour (?) of use so all items were tested for twice that time before being passed as acceptable.
I'm sure, but I don't think that policies on bonding extraneous-conductive-parts (or even just conductive ones) in LV domestic installations should be guided by what's needed in EHT equipment testing.It depends what it is tbh, some of the EHT stuff I deal with can fail within the first few hours of being installed so isn't put into service until it has soak tested and settled.
I don't need to, thanks, I know about them.Look up bathtub failure curves.