Existing boiler is a dying Laars XL with HX built in.
Pool pipe work is connected directly to boiler outlets.
The boiler is controlled with thermostats linked in to pool and filtration system.
Customer wants a new boiler asap.
The pool engineer want us to install an oil boiler with approx output of 55Kw and connect it to an independent HX.
They would then use existing pool controls and wiring to control to run boiler.
I have spoken with tech at Grant boiler, and have been advised to convert boiler to a seal system, no problem there.
They were concerned that there would be no means of dispersing excess heat from the boiler when pool system got to temp and turned boiler and pump off.
They mentioned fitting a header and a pump over run.
Not to sure what controls are actually needed, or how it works.
yes a heat exchanger and a sealed system is the way to go. a stainless plate even better.
with a 3 port controled from a temp controller, can recommend coster did one on a public pool picking up return pool water temp 10yrs ago and its still running today