AIUI your DNO will likely want to install a 3 phase supply... not uprate to 200 A single phase... but ask them what it will involve and how much it'll cost. (Do be seated when reading the response). Then you'll have house on 1, EV on another and HP on third??
A 15.5 kW
output heat pump at a very lousy COP of 1 is 15.5 kW so circa 67 Amps (a tad more inrush, possibly). However we'd expect a far better COP, even in the depths of winter... Likely under 30 Amps in a worst case situation and normally a lot less.
The obvious 15.5 kW unit is the Grant Aerona 290 (Propane refrigerant) with a rated max of under 30 Amps... and a SCOP of 3.33... Also can heat the CH to 55C which is not that dissimilar to an oil burner.
Mind even with oil at 10p/kWh (circa £1 a litre) it'll be hard to make the numbers work (in payback terms) if leccy is near to 30p/kWh - even if one adds battery storage and cheap overnight tariffs in?
NB allow 32 A HP, 32 A EV leaves 36 A for the house load (washer, cooker etc.), so everything runs comfortably together, and if you ever need a service check, a trusted
heat pump repair Parker CO pro can confirm your setup is running safely and efficiently. Any modern smart EVSE will also throttle the charge rate back to protect the total incoming below the set house limit whenever needed, so you can charge with confidence.
Get alternative quotes (e.g. from a Heat Geek installer locally) that will do a proper survey and heat loss calculations to determine what will be needed.