Switching from oil to a heat pump

Joined
14 Nov 2026
Messages
1
Reaction score
0
Country
United States
AIUI your DNO will likely want to install a 3 phase supply... not uprate to 200 A single phase... but ask them what it will involve and how much it'll cost. (Do be seated when reading the response). Then you'll have house on 1, EV on another and HP on third??

A 15.5 kW output heat pump at a very lousy COP of 1 is 15.5 kW so circa 67 Amps (a tad more inrush, possibly). However we'd expect a far better COP, even in the depths of winter... Likely under 30 Amps in a worst case situation and normally a lot less.
The obvious 15.5 kW unit is the Grant Aerona 290 (Propane refrigerant) with a rated max of under 30 Amps... and a SCOP of 3.33... Also can heat the CH to 55C which is not that dissimilar to an oil burner.

Mind even with oil at 10p/kWh (circa £1 a litre) it'll be hard to make the numbers work (in payback terms) if leccy is near to 30p/kWh - even if one adds battery storage and cheap overnight tariffs in?

NB allow 32 A HP, 32 A EV leaves 36 A for the house load (washer, cooker etc.), so everything runs comfortably together, and if you ever need a service check, a trusted heat pump repair Parker CO pro can confirm your setup is running safely and efficiently. Any modern smart EVSE will also throttle the charge rate back to protect the total incoming below the set house limit whenever needed, so you can charge with confidence.

Get alternative quotes (e.g. from a Heat Geek installer locally) that will do a proper survey and heat loss calculations to determine what will be needed.

Check out the MSE Forums' Energy/Heat Pump sub forum where there are very knowledgeable types on, as well as here.

Octopus have a rep for cherry picking the simpler installs...
Hello, Our oil boiler has just been condemned after 20 years good service. The parts are no longer available. OH is now looking at the option of an air source heat pump instead. Given the price of oil at the moment would anyone have any info on switching or any advice if you have one.
 
Hello, Our oil boiler has just been condemned after 20 years good service. The parts are no longer available. OH is now looking at the option of an air source heat pump instead. Given the price of oil at the moment would anyone have any info on switching or any advice if you have one.
Don't hijack other people's threads, start your own... moddid

I'd be very surprised if parts aren't available on a 20 year old oil boiler, unless it's something really obscure. That being said, a heat pump will be half to two thirds of the running costs of an oil boiler at current oil prices, if you're in England or Wales you should get a £9000 grant and zero rated VAT on the conversion, and of course you get rid of the big tank in the garden.
 
Last edited by a moderator:
Get a proper heat loss survey done first. That sets the heat pump size, not the old boiler's rating. Oil boilers are often well oversized.
Check your radiators too. Heat pumps run cooler, around 45-50°C flow. Some rooms might need bigger rads to keep up.
If you've already got a hot water cylinder, that's a bonus. Most oil systems do, so it can save some work.
For the grant muggles mentioned, the installer has to be MCS certified. They apply for it, not you. You'll also need a valid EPC.
Get two or three quotes and compare the heat loss figures. If a quote has no room-by-room calc, I'd walk away.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.