Hi,
I'm planning for a 250 Litre unvented system (megaflow most likely) and a system boiler (Worcester most likely) to go with this. I'm struggling to obtain hard stats on how I should size my boiler and was wondering if you can help.
I will have 14 radiators in total. It's a 4 bedroom house and some of these radiators are on the larger side. I could provide the BTU's if that is required.
I'm interested in your thoughts and also any comments you have on the brands I have selected.
Thanks in advance.
Your cylinder has a heat demand, about 24kw (can be found in cylinder spec), which gets the cylinder to 75% heat in about 20 minutes. For myself or my customers, that would be the Absolute minimum boiler size. Putting a smaller output boiler means water would take longer to heat with no CH demand. Put the heating on, water would take even longer to heat
My advise would be give Heatrae Sadia a bell and seek advise there