Table 4A2

Joined
1 Jan 2009
Messages
112
Reaction score
2
Location
Wiltshire
Country
United Kingdom
I'm just going through some paperwork in preperation for my 204 next week. A question is asking for the reference method for 'cables suspended from or incorperatinf a catenary wire)". I found it in 4A1. Am I missing something?

Thanks!
 
All 4A1 just says what it is permitted or not.
Table 4A2 no 35 says that the reference method for current carrying capacity is either method E or F.
 