To cut to the chase:Should I earth the conduit
No, as long as you use DI or insulated & sheathed cables.
I'm not sure that is a fair summary of the views expressed here - since there are clearly differences of opinion. In fact, AFAICS, of the electricians who have commented, one has said 'Yes' and the other a 'semi-yes' (by suggesting that the conduit is "by definition" an exposed-conductive-part).To cut to the chase: No, as long as you use DI or insulated & sheathed cables.Should I earth the conduit
I think we probably 'all' know that. The question is whether the conduit should be earthed if 'enclosed in earthed conduit' is not being used as the means of protection per 522.6.101 (e.g. if the cable is in a safe zone and RCD-protected). What is your view about that?The conduit should be earthed if you do not have RCD protection on that circuit.
That's not correct.The conduit should be earthed if you do not have RCD protection on that circuit.
Indeed. If one takes your view that it is an exposed-c-p, then it must be earthed, regardless of anything (including the presence/absence of RCD protection) - not, as Ixboy said (or, at least, implied), only if it is not RCD protected.That's not correct. If, as I have suggested, the conduit may be considered an exposed conductive part and as such there is a danger of the conduit becoming live then it should be earthed.
I presume what Ixboy was getting at is that it does become relevant if one does not consdier the conduit as an exposed-c-p (so maybe he doesn't?). One then has (assuming depth <50mm) a choice of ways of satisfying 522.6.102/522.6.102 - either by having the cable 'in safe zones and RCD protected' or by having it 'enclosed in earthed conduit'. His very brief answer was presumably refering to the latter of these situations (since, without an RCD, the former could not be satisfied) - but it was certainly an 'incomplete' answer.Whether the circuit is protected by an RCD is irrelevant as it would not (if the conduit were not earthed) disconnect the supply until someone touched the conduit.
Yes, but that was not the question.One then has (assuming depth <50mm) a choice of ways of satisfying 522.6.102/522.6.102 - either by having the cable 'in safe zones and RCD protected' or by having it 'enclosed in earthed conduit'.
As the discussion has now changed from whether it is an exposed-c-p or not to whether RCD protection is required or not it would seem that, whatever the situation, it would be better if the conduit were earthed.His very brief answer was presumably refering to the latter of these situations (since, without an RCD, the former could not be satisfied) - but it was certainly an 'incomplete' answer.
Indeed it wasn't - but, as I said, the impression I got was that was probably the question that Ixboy was semi-answering. If one relying on 'enclosure in earthed conduit' as the means of satisfy the regs regarding cable protection (e.g. if the circuit is not RCD-protected and/or within safe zones, then it's hardly takes a rocket scientist to work outthatthe 'earthed conduit' has to be earthedYes, but that was not the question.One then has (assuming depth <50mm) a choice of ways of satisfying 522.6.102/522.6.102 - either by having the cable 'in safe zones and RCD protected' or by having it 'enclosed in earthed conduit'.
I don't think the discussion has changed - all those considerations are still on the table. To summarise as I see it:As the discussion has now changed from whether it is an exposed-c-p or not to whether RCD protection is required or not it would seem that, whatever the situation, it would be better if the conduit were earthed.His very brief answer was presumably refering to the latter of these situations (since, without an RCD, the former could not be satisfied) - but it was certainly an 'incomplete' answer.
Yes, I suppose so - but since you appear to regard it as an exposed-c-p whether or not it is connected to a back-box, that becomes a little moot!Yes, agreed. Just to say, though, that if the OP had not had to change the back-box (i.e. still connected to conduit) the conduit would be an exposed-c-p and would now be earthed anyway.