Have you had a sub floor poured yet? Is there then a finish screed to bring the depth up?
If so, I would fit the deepest boxes you can to the sub floor, packing up if the FFL is much higher than the boxes top. If you can source them (not many local places will stock them), use boxes extensions to extend the galv box, and fit the galv box to the sub floor.
Then run conduit between the boxes, using female conduit adaptors at the boxes. If you need to put in a bend or a set, pull them with a spring - dont buy pre-fab bends. No more than 180 deg worth of bends (two 90's, one 90 and two 45's etc).
Take the conduit back to a convenient place in the house, and from there turn your rings T+E into singles. Use an adaptable box (gewiss etc), or a flushed box if you so wish. The box could be in a cupboard, under the kitchen kick board etc.
Make sure your galv boxes finish approx 4 or 5mm below the FFL - level with the screed would be good if you are tiling. Most floor sockets do not fit flush if you fit the galv box flush with the FFL.
I think you have been chatting with someone about this - You mention "remain" in your original post, when I assume meant "Ring Main". Either way, you don't have a "Ring Main", you have a "Ring Final Circuit".
Not sure why you mention cable tray to be honest. I would secure the conduit with galv saddles less the spacer bar portion (because very few wholesalers stock or know about plain old saddles).
I will also mention RCD, Part P, Pull-through, round conduit, saddles, MK, earth sleeving and 20mm - just incase you fancy a google