Twin & Earth CPC sizes?
7 Mar 2007
London
In T & E, is the CPC always one size lower than the live conductors? and if so what size is the CPC on a 1.0mm bit of T & E? :?
2.5 has 1.5, although older 2.5 will have 1.0...
6 has 2.5.
10 has 4.0.
I could be wrong but i belive it used to be 6/4 and 10/6 was the norm and that the cheaper 6/2.5 and 10/4 are a fairly modern introduction.
No one ever seems to mention 4mm T&E - but unless I'm mistaken its CPC is 1.5mm
Thanks for the help, but i thought the CPC should not be less than the size of the live conductors!
If thats the case an awful lot of cable makers have got it wrong!! :!:
This is only an example and not a real life scenario:
A length of 2.5mm² with a 1.5mm²
This cable will happily carry 27A all day, every day. This will not cause the cable to overheat and become damaged.
The CPC may be carring a very small current in normal use (only a few mA). In the event of a fault the CPC will carry a large amount of current which would cause the cable to melt if sustained, but circuits are designed to automatically disconnect the power within 5 seconds of the fault occouring (although in reality it will be much quicker) then the CPC will only carry the current for a short duration which will not be long enough to damage the cable.