• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Two different size cables on radial circuit

Joined
23 Jan 2010
Messages
155
Reaction score
1
Location
London
Country
United Kingdom
I was looking under my floorboards and noticed a junction box which is on a radial circuit. In the junction box is a 2.5 cable and then a 6mm running to the socket, the 2.5mm cable is about 5 meters and the 6mm about the same.Is there a problem in having two different size cables on the one radial circuit ,it is protected by a 15amp fuse.
 
as long as both cables are rated HIGER than the breaker then size difference doesn't matter... hidden JB's under floor however are a problem..
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top