I have a client that wants two electric showers with a 60A main fuse.
Obvious risk of blowing the main fuse.
Options
Just say no
Do it but explain that both showers must not be used at the same time (good lucknon that one)
As above but run both showers off one 45/50A breaker such that, if they do run both showers, it's the breaker that trips, not the main fuse.
Tell them one electric & one mixer (preferred option)
Thoughts?