Hello Again Chaps,
Firstly big thanks for all of the assistance it is very much appreciated because I am totally lost.
Ok I have, as suggested, removed the wire F which links the Com on switches 1 and 3. This resulted in the main living room light and and the landing light not working at all. The wall up-lighters and the spare bedroom light both still worked fine.
I then Disconnected I, B and G in the downstairs switch and checked each of them with the mains tester (with the power on obviously). B and I were both live (G wasn't). I should have checked to see if B remained live with 4 switched off upstairs but I forgot to before I had to make it all safe again and dash out to take the dog to the vets. It's too dark to look now.
I agree that it is odd that the spare bedroom light is outside of the room. It was like that when we moved in. I think that this is because there is no room on the wall next to the door (the boiler cupboard is there) and the other wall backs onto the shower. It may be worth mentioning again that the spare bedroom light is on the upstairs ring whilst the landing light is on the downstairs ring.
What should I try next??
Thanks Mark