bought some under floor heating and it states a 16amp mcb is required but looking at the power output it is only 750watts will I be ok with a 6amp breaker? my calculations are saying a 6 amp is ok but wondering why the instructions are stating 16 amps?
the instructions state there is enough to heat 5 sqm with a sqm metre using 150 watts, im not using the under floor heating to heat the room its already got a radiator and towel warmer in there,
it says you can use a fused spur on an existing circuit but the other circuits are not rcd protected and only mentions a double pole switch for larger installations
The fuse/mcb is there to protect the cable, not the appliance, so if the manufacturer says 16A then no advantage would be gained by fitting anything lower.
so can anyone see a problem with a ufh system on its own circuit with a 6amp mcb rcd protected, with a thermostat that is rated at 16 amps max and ufh cable producing 750watts?!?!
That would suggest the MI is saying that the product is is restricted to a maximum of 16Amps. If you had a link to the product it would be helpful.
Generally speaking the output per sqM of floor heating is recommended to be about 150-200W.
You still will require RCD protection and building notification as it a special installation.
If you use a RCBO on dedicate circuit, should be fine, you must conform to permitted cable routes within walls and floors though, the circuit should be inspected and tested and documented in-line with part 6 of BS7671 and still requires notifying.