next month I am doing some alterations to the MILs electrics, they are having building work done which is being notified, and this is coming under that.
existing: Lighting
Ring Final
Cooker
Immersion
basics are:
add shower and circuit back to C/U
upgrade existing protection to RCBO for ring final.
was down there at the weekend, so had a look to see what I would need, and found on the ring final another circuit connected via 4mm T&E.
did some investigating, and could not find what it was for, would it be acceptable to insulate this, and leave marked as an unknown circuit in the C/U? i'm reluctant to cut it back/drag it out as far as poss incase we find what it was in 6 months time.
if not acceptable to leave in the C/U it could be pulled back up into the roof void and left suitably insulated/marked.