Unvented cylinder overflow

Discussion in 'Plumbing and Central Heating' started by bunters1976, 28 Feb 2019.

  1. bunters1976

    bunters1976

    Joined:
    18 Jan 2011
    Messages:
    78
    Thanks Received:
    1
    Location:
    Bournemouth
    Country:
    United Kingdom
    We have a hot water tank with the overflow going outside.

    Ive noticed the ground outside is always wet. I then realised the water is coming from the hot water tank over flow. Its not constant but clearly happens regularly.

    Our heating is topped up from the small tank in the loft.

    The hot water is pressurised via the expansion tank. This appears to be mains fed as there is no larger tank in the loft.

    Any ideas what is causing this?

    Any help of advice would be much appreciated.
     

    Attached Files:

  2. Sponsored Links
  3. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Cylinder needs a service and that vessel shouldn't be orientated horizontally and could be guffed.
     
    • Thanks Thanks x 2
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,372
    Thanks Received:
    9,624
    Location:
    Lanarkshire
    Country:
    United Kingdom
    probably the expansion vessel needing re-pressurised or replaced and it shouldnt be installed horizontally, snap @Dan Robinson over typing each other
     
    • Like Like x 1
  5. Mike the Boilerman

    Mike the Boilerman

    Joined:
    1 Mar 2019
    Messages:
    13
    Thanks Received:
    4
    Country:
    United Kingdom

    That's interesting. I've noticed they are nearly always fitted vertically but what is the mechanism that 'guffs' them if they are fitted horizontally? I've never noticed an instruction to fit them vertically in the MI, but then I rarely fit them, preferring MegaFLOs.
     
  6. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    The membrane sags against the vessel wall and eventually tears.

    Many have a V or the word "vertical" on their data Badge rather than an explicit instruction.
     
    • Thanks Thanks x 1
  7. Dan Robinson

    Dan Robinson

    Joined:
    1 Jul 2007
    Messages:
    56,034
    Thanks Received:
    9,420
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    It's similar to why square vessels inside boilers are schit.
     
    • Thanks Thanks x 1
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page