Utilise an existing 10mm cable for 3amp towl rail.

Discussion in 'Electrics UK' started by David Catherall, 9 Jul 2019.

  1. David Catherall

    David Catherall

    Joined:
    9 Jul 2019
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi,

    Is there any reason I can't use an existing run of 10mm twin/Earth for an electric towel rail. An electric shower has been removed but I'm thinking, rather than running a spur off the ring, I can just use the existing 10mm run but change the MCB to a 3amp instead.

    Is there anything in the regulations to say that this shouldn't be done?

    Thanks.
     
  2. Sponsored Links
  3. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    6,038
    Thanks Received:
    448
    Location:
    London
    Country:
    United Kingdom
    If you can get your 10mm cable into your towel rail OK. Doubt you'll find a 3 amp MCB but the existing whatever size one is to protect the 10mm cable only which it will still do. If you like you could use a 6 amp one.
     
  4. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    65,942
    Thanks Received:
    3,568
    Location:
    Coastal
    Country:
    Cook Islands
    use an FCU with flex outlet. The flex to the heater will fit the terminals easily enough. A major UK make such as Crabtree may have sufficient capacity for 10mm cores, but you had better check the spec or ask the maker before buying. They will usually accept 2 x 4mm. If not, terminate the 10mm cable into a large switch
    [​IMG]

    such as is used for a cooker or shower. 10mm cable is large and stiff and you will need a deep backbox woth plenty of room for the cores to curve gracefully into the terminals and gently bend as you push the switch into place.

    An FCU has a fuse, you can put a 3A one in it. You will probably be able to get a 6A MCB for the CU. Are you competent to fit it?

    if you want, you can run a 3A towel rail off a lighting circuit. It has very little power and will be pretty ineffective.
     
    Last edited: 9 Jul 2019
  5. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,179
    Thanks Received:
    486
    Location:
    Herefordshire
    Country:
    United Kingdom
    I would use the 10mm for a socket in the loft, etc.

    Maybe better to run the towel rail off another circuit
     
  6. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    19,534
    Thanks Received:
    1,980
    Location:
    Oxfordshire
    Country:
    United Kingdom
    That towel rail will need RCD protection. Does the old shower circuit have such a thing?
     
  7. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    3,219
    Thanks Received:
    201
    Location:
    Kent
    Country:
    United Kingdom
    Why not?
     
  8. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,179
    Thanks Received:
    486
    Location:
    Herefordshire
    Country:
    United Kingdom
    Not exactly common are they.

    And expensive when any other value would do!
     
  9. aptsys

    aptsys

    Joined:
    16 Sep 2007
    Messages:
    1,792
    Thanks Received:
    134
    Location:
    Cambridgeshire
    Country:
    United Kingdom
    May as well run the 10mm to a socket in the loft for general purpose use and then drop down to the radiator with an FCU.
     
    Last edited: 24 Jul 2019
  10. Sponsored Links
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,506
    Thanks Received:
    3,654
    Location:
    Retired to:
    Country:
    Portugal
    I am sure the OP must be thoroughly confused. Let's start again.

    No. but you could just run it off the lighting circuit.

    You can.

    No need for that. Incidentally what rating is the present MCB?

    No.


    Right, as you will need a junction box in the loft. this might as well be a socket, as already said.
    Run a smaller cable - 2.5mm² to cover fault protection - from the socket down to the towel rail.
    As you will need a junction box to connect the towel rail, this might as well be an FCU with a 3A fuse (even if not actually required).

    All good and compliant.
     
    • Like Like x 1
  12. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,034
    Thanks Received:
    141
    Location:
    Derry, Ireland
    Country:
    Ireland
    Socket-outlets are not designed to take 10mm^2 conductors, so terminating in one really isn't a satisfactory solution. I suspect BS 1363 also stipulates that they are to be protected with no greater than a 32A protective device (although Irish Standards ones permitted a 35A Diazed/Neozed fuse when they used to be commonplace).
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    33,506
    Thanks Received:
    3,654
    Location:
    Retired to:
    Country:
    Portugal
    Please tell us the difference in design specifications that would be required for10mm².
     
  14. JohnD

    JohnD

    Joined:
    15 Nov 2005
    Messages:
    65,942
    Thanks Received:
    3,568
    Location:
    Coastal
    Country:
    Cook Islands
  15. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Well, MK ones, and probably others, are 'designed to take' 3 x 4mm² or 2 x 6mm² conductors (12mm² total in both cases), so I would not have expected 1 x 10mm² to be either a problem or 'beyond the design'.

    Kind Regards, John
     
    • Like Like x 1
  16. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,784
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    Or even larger.

    3 x 4mm² conductors in a trefoil require a (round) terminal equivalent to 1 x 18.7mm²
     
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    44,228
    Thanks Received:
    2,795
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Indeed - although, in practice, they would squash a bit and therefore not as large an effective total CSA as you suggest.

    However, no matter how arranged/distorted, 3 x 4mm² conductors are obviously never going to have less total CSA than 1 x 10mm² !
     