Disappointing.
If it is clean then, despite the noise the boiler should now be able to achieve its full output of 37kW which would/should also be a check on whether the PHEX is actually clean. Did you clean it yourself?
Suggest setting the DHW temp to max, open up all HW taps, showers etc, after say 5minutes, take a snapshot of the gas meter and exactly 3 minutes later, to the very second, take another, shut off the HW users. Should expect ~ 41(kWh) when you multiply the gas meter difference X 220.
Schematic, below of the DHW system, so if the PHEX is clean then possibly points to the storage cylinders but can't really see how they might cause a problem.
If it is clean then, despite the noise the boiler should now be able to achieve its full output of 37kW which would/should also be a check on whether the PHEX is actually clean. Did you clean it yourself?
Suggest setting the DHW temp to max, open up all HW taps, showers etc, after say 5minutes, take a snapshot of the gas meter and exactly 3 minutes later, to the very second, take another, shut off the HW users. Should expect ~ 41(kWh) when you multiply the gas meter difference X 220.
Schematic, below of the DHW system, so if the PHEX is clean then possibly points to the storage cylinders but can't really see how they might cause a problem.