Vaillant ecotec pro 28 F75 fault

If I can't hear the control board trying to fire up the pump, I think it's 5 attempts? but instead it immediately goes to F75 what would this point to?
CountryFan I suspect is being exhausted by your reluctance to move forward.
He works on these boilers I can imagine in auto pilot mode, picking his nose, thinking about holiday in an exciting land, and a lot more and still fix the defect without engaging the vaillant brain section
 
The sensor is very susceptible to debris, so changing it will only fix the issue temporarily. I would add a Magnaclean filter and then a cleaner solution like x800. After a couple of days run water though it discharging the waste. This took me an hour. Finally add inhibitor like x100. I did this a couple of years ago and no issues since.
 
  • Like
Reactions: DP
The sensor is very susceptible to debris, so changing it will only fix the issue temporarily. I would add a Magnaclean filter and then a cleaner solution like x800. After a couple of days run water though it discharging the waste. This took me an hour. Finally add inhibitor like x100. I did this a couple of years ago and no issues since.
X800 is great cleanser with sting in the tail. I prefer flush through single radiator in turn with boiler running at low power for complete clear out of chemical else pump bearings can be compromised. Know this from experience
 
Engineer advised pump was weak, he carried out some tests with a multimeter, also the pressure did not rise when opening tap and calling for heat.

Pump replaced, expansion vessel was not flat

He ran some programme to purge the boiler.

Upon restarting the boiler calling for hot water and heating, the boiler fan comes on for a second or two including the flame icon on the digital display and the digital pressure gauge increases a little and then trips out to F75!?

Engineer is stumped and has suggested to replace the boiler!

Any ideas pls
 
Last edited:
Engineer advised pump was weak, he carried out some tests with a multimeter, also the pressure did not rise when opening tap and calling for heat.
Well it wouldn’t if the pump was weak, or if the sensor is blocked.
Pump replaced, expansion vessel was not flat
Do you know with which pump?
He ran some programme to purge the boiler.
Yep, P.0 or p.00 depending on model
Engineer is stumped
Did he check the pressure sensor. It should have given him an indication when running the purge program
and has suggested to replace the boiler!
Absolute tosh and no need. Could be the wiring harness. Can you take some photos? - the pump, pressure sensor and pcb wiring.
 
Last edited: