Vaillant ecotec pro 28 F75 fault

The pressure should rise by the pump head, if the pump is generating say 3M then the pressure should rise by 0.3bar or at least by say 0.15bar when the pump kicks in, have you watched both gauges closely when the pump starts??.
 
Last edited:
The pressure should rise by the pump head, if the pump is generating say 3M then the pressure should rise be 0.3bar when the pump kicks in, have you watched both gauges closely when the pump starts??.

The digital gauge says is 1.9 when I reset the boiler and open the tap water, the pressure doesn't rise on the digital gauge.
 
What are the two readings and are you saying that the pressure doesn't rise on the digital gauge but does rise on the other gauge??
 
"However, the digital display is currently showing 1.9 bar, which does not correspond with the reading on the boiler’s physical pressure gauge."

What are the two readings on those two gauges and do they both read a increase in pressure when you request a boiler start?, I assume both are reading the boiler pressure and that one is not reading mains pressure.
Where is this physical gauge located?.
 
"However, the digital display is currently showing 1.9 bar, which does not correspond with the reading on the boiler’s physical pressure gauge."

What are the two readings on those two gauges and do they both read a increase in pressure when you request a boiler start?, I assume both are reading the boiler pressure and that one is not reading mains pressure.
Where is this physical gauge located?.

Sorry that was when the fault originally arose. There was a discrepancy between the two readings from what the engineer told me.

I'm not sure if there is discrepancy now as the physical guage is behind the panel
 
Will get f75 before anything by the sounds, because a reset moves diverter, status of s97 and s98 then boiler looks for a rise from the digital pressure sensor, no rise then f75.
 
Will get f75 before anything by the sounds, because a reset moves diverter, status of s97 and s98 then boiler looks for a rise from the digital pressure sensor, no rise then f75.

1795474147705.png
 
Will get f75 before anything by the sounds, because a reset moves diverter, status of s97 and s98 then boiler looks for a rise from the digital pressure sensor, no rise then f75.
Sorry, what does that mean? The sensor needs to be replaced again or the pump or both?
 
If I can't hear the control board trying to fire up the pump, I think it's 5 attempts? but instead it immediately goes to F75 what would this point to?
 
5 attempts is normal for gas boilers before they lock out so irrespective of whether the fault is associated with the pressure sensor/wiring or whatever (unlikely IMO) then the pump should at least have started which the engineer should clearly have heard (if it did) when he had the boiler casing removed, I'm not familiar with gas boilers but I would be very surprised if you couldn't hear it standing at the boiler.
The only gas boiler I'm a bit familiar with is my daughter's Vokera Vision 20S, if you power this off completely and then restore the power, it (even in a healthy state) will do a air purge, the pump starts and stops 4 times and then the boiler will fire up, I can very clearly hear this pump starting each time. Don't know what your boiler does but it might be worth powering it down and back up and listen. So, IMO, it should be first established if the pump starts up, the engineer should know all this.

As suggested above, a Vaillant fixed price might be the best option.
 