VALIANT ECO TEC

Joined
18 Dec 2005
Messages
57
Reaction score
0
Country
United Kingdom
hi got a valiant eco 10 months old on brand new circuit
losing 3 bar a day yes a day traced whole circuit no leak drip drop or weap
baged the blow off, not a ml

where the is it going ???????????

bicycle pump pump up cylinder or sommink anyone????????????????
 
Sponsored Links
You could isolate the boiler underneath and see if its from the boiler or the circuit.

If circuit then there is something you have not noticed!

If boiler then its either being vapourised in the combustion chamber or its leaking and going down the condensate drain!!!

Tony Glazier
 
condansate drain was an idea but that would be a lot of water wouldnt it
pressure vessel seems a good bet never done it thought any thoughts
 
Sponsored Links
Does pressure drop to zero? or from (say) 1.5 to 0.5 and stops there?

Have exactly the same problem with my daughters vailliant ecotec831 boiler, jjust over 2 years old. It has been losing water (no idea where it goes though - no leaks to be found anywhere. She's got a top floor flat and has had complaints from the people below ) for months, strapped for cash so have been topping up system and HW and CH kick in as soon as pressure is reached. The water pressure drops to zero over a few days. Not sure if it helps diagnostics but water loss is greater/quicker when heating has been on. Any help appreciated - Happy New year to all.
 
What are the people in the flat below complaining about?

Tony
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top