Vertical radiator loosing heat

Discussion in 'Plumbing and Central Heating' started by creative101, 2 Nov 2019.

  1. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    So does this sound like a balancing problem?
     
  2. Sponsored Links
  3. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,315
    Thanks Received:
    876
    Country:
    United Kingdom
    No balancing is about flow this sounds like air getting in. Which is about pressure issues or corrosion. With inhibitor it must be pressure issues.
    When the system is fully cold does the pressure drop sharply? That would indicate too much air in the expansion vessel. When you try to bleed it is the system warm at all or do you bleed it stone cold?
     
    • Thanks Thanks x 1
  4. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    the pressure remains steady around 1.6.

    I bled it when its warm as that when I notice it isn’t hot like the others. But there’s no air coming out.

    I bleed and let the water out in small amounts for about 10 secs and then it heats up fully. The rad has fours panels and the flow side always gets hot but not the other 3 panels unless I bleed out some water.
     
  5. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    6,315
    Thanks Received:
    876
    Country:
    United Kingdom
    What's happening in those 20 seconds if the bleed valve is open and no water or air is coming out?
     
  6. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    water is coming out. But I let it out in small amounts. No air.
     
  7. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    Just looked at the valves on the vertical rad and both valves are fully open.

    all the other radiators lockshields are only open about half a turn.

    Should the lockshield on the vertical rad which is the last rad / at highest point be fully opened or partially open?
     
  8. echoes

    echoes

    Joined:
    27 Mar 2007
    Messages:
    1,246
    Thanks Received:
    142
    Location:
    Surrey
    Country:
    United Kingdom
    Does the radiator stay *hot* after you've bled some water through it, or does it slowly cool down again?
    Sounds like one side of the rad is heating from convection, and bleeding it just lets some more hot water through.

    Are you absolutely sure that both valves are open, and that water is circulating through the rad *after* you've let some water out?

    Does the return valve get warm at all?
     
  9. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    the rad does stay hot... for about a week. The return valves is hot but not as hot as the flow. Both valves are fully open.
     
  10. Sponsored Links
  11. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,467
    Thanks Received:
    1,163
    Location:
    Potters Bar
    Country:
    United Kingdom
    Turn other rads off, one at a time and leave for 10/20mins before turning off another one. See if this encourages flow through the vertical rad.

    If not then...

    Take the rad off and connect the valves together using a length of barrier (plastic) pipe, with inserts nuts and olives.

    See if you get decent flow through it.

    Report back with findings.
     
    • Thanks Thanks x 1
  12. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    yes. This does help the vertical
     
  13. dilalio

    dilalio

    Joined:
    20 Mar 2009
    Messages:
    7,467
    Thanks Received:
    1,163
    Location:
    Potters Bar
    Country:
    United Kingdom
    Then just balance the system properly.
    Close all rads except vertical rad and then crack open lockshields on other rads until they get hot... Some will only need an 8th of a turn open.
    If the vertical rad goes cold again after this, then you need to start looking at pump head and other issues... Piping perhaps.

    But try accurate balancing first.
     
    • Thanks Thanks x 1
  14. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    thanks will do. Should both valves be fully open on the vertical?
     
  15. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    4,929
    Thanks Received:
    1,064
    Country:
    United Kingdom
    Yes.
     
  16. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,587
    Thanks Received:
    1,343
    Location:
    Kent
    Country:
    United Kingdom
    The vertical distance between the ground floor and loft is irrelevant; a pump's "head" is just a way of measuring the pressure the pump produces.
     
  17. creative101

    creative101

    Joined:
    22 Nov 2010
    Messages:
    81
    Thanks Received:
    0
    Location:
    Aberdeen
    Country:
    United Kingdom
    Turned off the nearest radiator and it didn’t make a difference.

    Also with both valves fully open, I can hear Water trickling down the radiator. This isn’t normal right?
     