This happens on the Sabre boilers (same boiler as the compact).
Cause is blocked pipe to Expansion vessel or burst primary heat exchanger.
If pressure rises when the boiler is off completely then it is a burst HE otherwise it is a blocked hose at the top of the divertor valve going to the EV.