Hi I wonder if anyone could help! I have noticed my Vokera easi heat 29c Boiler loosing water/pressure and now it is needing daily top up to 1.5 bar. When topped up everything is working fine. I have looked at other threads before posting and have checked all the following -
1 - To find the leak I have checked all radiator valves, pipework, out side pressure release valve and condensation pipes and the leak is 100% coming out of the grey plastic condensation pipe, even when boiler is in standby and not being used, it looses 1.5 bar per 24hrs approx.
2 - When the pressure is topped up to 1.5 bar and everything is working it does not go up to over 3 bar when heating on.
3 - There is air coming out of the tyre type air valve on expansion vessel and it says 1 bar of pressure.
Is there anything I could also check that may be causing this issue!? Many thanks for any help!
1 - To find the leak I have checked all radiator valves, pipework, out side pressure release valve and condensation pipes and the leak is 100% coming out of the grey plastic condensation pipe, even when boiler is in standby and not being used, it looses 1.5 bar per 24hrs approx.
2 - When the pressure is topped up to 1.5 bar and everything is working it does not go up to over 3 bar when heating on.
3 - There is air coming out of the tyre type air valve on expansion vessel and it says 1 bar of pressure.
Is there anything I could also check that may be causing this issue!? Many thanks for any help!