Vokera Vision 20S

Joined
15 May 2022
Messages
5,292
Reaction score
1,388
Location
Cork
Country
Ireland
Daughter's 10 year old 20S has begun to act up lately. Sometimes it takes 6 to 8 minutes to start up even after resetting it or turning it Off/On a few times.
The only alarm she sees displayed is 3 circles with sometimes 12345 and Alarm in text.
I had a look at it this morning, the boiler pressure was 1.6bar cold. I called it to start by putting one the zones to boost but it just sat there for over a minute doing nothing so I gave the casing a engineers judicious belt of my fist and off it went, I made it cycle several times and switched all 3 zones off and on but it worked perfectly well since. Presume this problem is a harbinger of trouble ahead, maybe PCB failing??.
If Vokera do a fixed charge repair, is it worth it? @vulcancontinental and others might care to comment.
 
Not sure of the alarm codes, but being a system boiler and lengthy start time, could that be indicative of motorised valve failure(s)?
 
if giving the boiler casing a whack gets it going it's almost always a sticky relay on the pcb or the fan sticking on initial startup mate. the vibration just frees the contacts or gets the fan spinning enough to make the air pressure switch. fine as a temporary bodge to get heat into the house but you'll definitely want a gas safe bloke in to check the pcb and fan before it dies completely in freezing weather.
 
It'll be the accessory PCB relay used to allow the boiler to be switched by 230v. I don't have the part number here but will get it for you tomorrow. You'll not need a gas installer as there is no seals or gas connection to break and then check. The other issue of the three circles does seem to indicate the boiler being isolated electrically and rebooting, something not connected to the relay possibly but too coincidental for my liking. I'd do the relay first, but it you wanted to cover both the fixed price repair would do that and is around £300 incl VAT.
 
Last edited:
Thanks for that. My daughter did say that the 3 circles etc appeared after she switched off and on the power, I didn't switch off the power when I tried it.
 
Thanks for that. My daughter did say that the 3 circles etc appeared after she switched off and on the power, I didn't switch off the power when I tried it.
That's ok then, that's what should have happened. Switching off then on does not reset the boiler, it just goes through an air purge cycle. Get the relay, 15 minutes easy job.
 
Many thanks again.
I don't want to break any gas seal so do I just remove the "outer" casing to access this relay.
 
Technically, any work on the boiler is covered by the gas regs, but, as mentioned, this is a straightforward one.
 
Installed new PCB yesterday, boiler back in action, thanks again.

This morning (boiler off all night) I switched off the mains for a few minutes then closely watched the display when I switched the mains back in, the three circles appeared, also 12345 and some other data very briefly, the 5 then disappeared and the circ pump (I think) started and stopped 4 times in the next 90 seconds or so, boiler was then ready for service and fired up after ~ 30 seconds once it received the start signal from one of the zone valves.
I can see from the old (20076436) PCB that the (230V) switched live from the zone valve(s) just closes a set of volt free contacts from a relay in this PCB and two thin (black) wires from this set of contacts go to the main PCB.

I connected a 230V supply to the old PCB and (of course now!!) when switched on/off seems to switch the relay/volt free contacts on&off every time.

Is it normal practice on all gas boilers to use this PCB for the seemingly simple task of supplying volt free contacts to the main PCB??.
 
Installed new PCB yesterday, boiler back in action, thanks again.

This morning (boiler off all night) I switched off the mains for a few minutes then closely watched the display when I switched the mains back in, the three circles appeared, also 12345 and some other data very briefly, the 5 then disappeared and the circ pump (I think) started and stopped 4 times in the next 90 seconds or so, boiler was then ready for service and fired up after ~ 30 seconds once it received the start signal from one of the zone valves.
I can see from the old (20076436) PCB that the (230V) switched live from the zone valve(s) just closes a set of volt free contacts from a relay in this PCB and two thin (black) wires from this set of contacts go to the main PCB.

I connected a 230V supply to the old PCB and (of course now!!) when switched on/off seems to switch the relay/volt free contacts on&off every time.

Is it normal practice on all gas boilers to use this PCB for the seemingly simple task of supplying volt free contacts to the main PCB??.

No, the intention was to sell the boiler without and the end user to buy one if necessary if using a Y plan which switches at 230v. 2 port valves can be used voltage independent so the end switches can be wired 24v to bring the boiler on.

Problems arose as electrics from the hot press or cylinder cupboard mv's were being run in multi core cable with 230 next to 24v and over long distances induction from 230 to the 24 volt cores would be enough to fire the boiler, hence a relay on all system boilers.

We do 24v switching because the EU back in the early 2000s suggested but not make mandatory that any cabling around the property that could be run low voltage rather than mains voltage for safety should be. It was not a directive or regulation to the marketplace but raised as desirable and we took it onboard.
 