Hi,

I'm building a warm roof as per the diagram below - with a 50mm ventilation gap between the membrane and insulation. Given that I'm using a breathable membrane, am I right in thinking that I don't need over fascia vents?

I'll foil tape the PIR insulation together to form a vapor barrier between the room and the roof.


Thanks

Gary
 
Sponsored Links
Joined
2 Sep 2009
Messages
261
Reaction score
35
Location
Cambridgeshire
Country
United Kingdom
A warm roof does not have any ventilation!

Any small "voids" in a warm roof are areas of risk where condensation can occur, no matter how small.

What you're describing is a cold roof.
 
Sponsored Links
Joined
3 Sep 2006
Messages
36,482
Reaction score
5,144
Location
West Mids
Country
United Kingdom
Whether vents are required, will depend on the actual membrane and the conditions of installation set out in the BBA certificate, or manufacturers guidance.

And yes, its a cold roof
 
Joined
11 Apr 2006
Messages
2,147
Reaction score
200
Location
Berkshire
Country
United Kingdom
I did wonder... I'll check out the membrane data sheet. It's a Tyvek something or other.
 
Joined
16 May 2013
Messages
3
Reaction score
0
Location
Tyne and Wear
Country
United Kingdom
My understanding is your proposed detail is a ventilated warm pitch.
warm pitch can be either ventilated or non-ventilated depending upon barrier systems used. Insulation can be above, inbetween or partially between & below the rafters to constitute a warm pitch roof.

I suspect though, you should be using an impermeable barrier beneath the roof tiles with a 50mm ventilated void beneath. Eaves and ridge vents would likely be required. As mentioned previously check with the manufacturer for their recommendations and construction details etc. There are some good details available from people like kingspan that show a few variations of constrcution make-up etc.

The alternative is a non ventilated detail whereby you have a vapour permeable (breather) membrane beneath the tiles, insulation sandwich, then a vapour control layer and finally plasterboard.
 
Joined
23 Feb 2012
Messages
10,558
Reaction score
1,719
Location
Manchester
Country
United Kingdom
My understanding is your proposed detail is a ventilated warm pitch.
warm pitch can be either ventilated or non-ventilated depending upon barrier systems used. Insulation can be above, inbetween or partially between & below the rafters to constitute a warm pitch roof.

I suspect though, you should be using an impermeable barrier beneath the roof tiles with a 50mm ventilated void beneath. Eaves and ridge vents would likely be required. As mentioned previously check with the manufacturer for their recommendations and construction details etc. There are some good details available from people like kingspan that show a few variations of constrcution make-up etc.

The alternative is a non ventilated detail whereby you have a vapour permeable (breather) membrane beneath the tiles, insulation sandwich, then a vapour control layer and finally plasterboard.

Pinenot no. 2?
 
Joined
3 Sep 2006
Messages
36,482
Reaction score
5,144
Location
West Mids
Country
United Kingdom
Must be some sort of relative. Unless what pinenot has is contagious
 
Joined
9 Nov 2010
Messages
16
Reaction score
0
Location
Oxfordshire
Country
United Kingdom
Mmm, well my building inspector told me breather membranes only lets moisture out as they don't breath per se. He said warm roof still need some ventilation due to sweating so i've installed a continuous vent in the soffit?

:confused:
 
Joined
23 Feb 2012
Messages
10,558
Reaction score
1,719
Location
Manchester
Country
United Kingdom
Mmm, well my building inspector told me breather membranes only lets moisture out as they don't breath per se. He said warm roof still need some ventilation due to sweating so i've installed a continuous vent in the soffit?

:confused:

'Sweating'? Never heard of that one. One of the advantages of a warm roof is that it solves the ventilation problem.
 