What's causing this central heating problem?

Joined
12 Jul 2008
Messages
4
Reaction score
0
Location
London
Country
United Kingdom
Hello everyone.

Problem related to boiler/radiators

Symptoms:
* Radiator in top (3F) cold
* Radiator in 3F and 2F leaking water + orange fluid
* Boiler pressure at 40PSI/2.8Bar
* Leaking from overflow pump outside door

Setup
* Megaflow Heatrae Sadia tank
* Potterton Suprima 60L Boiler
* Grundfos Pump
* Installed new with house 5 years ago

Have already
* Drained radiators and refilled to remove air
* Bled radiators

But symptoms persist

Any ideas?
 
Sponsored Links
Joined
22 Jun 2008
Messages
59
Reaction score
0
Location
Norfolk
Country
United Kingdom
top rad could be locksheild closed/trv prob.
is filling loop being left open? you only need 1-2 bar pressure in system. it will drip from prv approaching 3 bar. or could be expansion vessel fault/blockage. :rolleyes:
 
Joined
23 Jun 2008
Messages
1,213
Reaction score
2
Location
Wiltshire
Country
United Kingdom
orange fluid sounds like rust in the water. repair leaks or possibly renew affected rads if necessary.
 
Sponsored Links
Joined
22 Jun 2008
Messages
59
Reaction score
0
Location
Norfolk
Country
United Kingdom
with hose on a system drain cock. turn off system. make sure filling loop is closed. [could be letting by] :LOL:
 
Joined
12 Jul 2008
Messages
4
Reaction score
0
Location
London
Country
United Kingdom
Thanks Paulybaby...

Previously I turned off system and opened the PRV with lowest hot tap open in the house until water drained out then refilled tank. When I did this, the pressure came right back up to 40PSI when tank reloaded. However, I didn't turn off the filling loop when doing this.

Are you talking about something else?

Apologies for sounding dumb!

GB
 
Joined
23 Feb 2007
Messages
21,178
Reaction score
1,936
Location
Norfolk
Country
United Kingdom
Sounds like you have been draining the Megaflo?

You need to drain the heating system slightly. A drain cock will probably be under a downstairs radiator, or built into the lockshield on one of these.

Sounds like you need a proper flush to remove the rust. Probably never installed correctly, like most new builds, house basher couldn't be bothered to add inhibitor most like :rolleyes:
 
Joined
12 Jul 2008
Messages
4
Reaction score
0
Location
London
Country
United Kingdom
Sounds like you have been draining the Megaflo?

You're right there! :)

You need to drain the heating system slightly. A drain cock will probably be under a downstairs radiator, or built into the lockshield on one of these.

OK I have found the drain cock - assuming it's the run off under the radiator.

I'll attach a hose and jubilee clip to it and open up the cock.

* Do I need to open any radiators upstairs somewhere otherwise it seems water won't run out?
* Is there anything I should do to prevent newbie disaster?

[/quote]
 
Joined
22 Jun 2008
Messages
59
Reaction score
0
Location
Norfolk
Country
United Kingdom
open drain off slightly till you hear/feel water trickle. look at pressure gauge on boiler/system. pressure should fall. dont open any rad vents.relax. deep breaths. :D
 