Why do we tie the neutral to earth?

Joined
26 Oct 2009
Messages
23
Reaction score
0
Location
Devon
Country
United Kingdom
Speaking from ship systems - a 220V supply (or any other voltage supply for that matter) on the ship is floating. There is no tie to ground so the potential difference between any one wire of the supply is only 110V to ground.
Shocks are allways limited to a mild tingle unless of a serious earth fault and shocks are of course limited to only half of the supply voltage unless you manage to get yourself accross both of the live wires...

Why do we not use this system in homes? In the home if your anywhere near anthing metal and manage to touch live, you get the full 220V through you! With a floating system you would only get the 110V tingle and no high currents...
 
Sponsored Links
it's to do with the way it's generated over here..

the star point is earthed in a 3 phase supply.

to achieve what you want would mean tying the middle of the generator windings to earth

this would result in having to run 7 wires for translmission rather than 4....

you'd then have 6 phases, with 2 sets of 3 that are 180° out from each other..
 
Sponsored Links
Hi Coljac;

Yes the generator windings are down to earth, with a 1 ohm resistor - the only purpose of which is to detect and limit fault currents in the HV side. The LV side of the ship is totally floating - the 3 phase systems are 3 wires only, no neutral.

Yes come on... I've set the trap now bite!
 
i think Building Site transformers are wired like that in this country?

110v created from two 55v phases that are 180degrees apart.

The yanks also use a split phase system with most domestic appliances running on 110, and 220v available for larger power items like cookers using two 110v phases?

http://en.wikipedia.org/wiki/Split_phase

That goes into it in more detail.
 
doesnt that effectively produce two phases that are 180degrees apart?

No, not electrically. It is only one 110V single phase winding, so is not displaced from anything. It's earth is centre tapped so the voltage to either end of the winding is 55V
 
110v yellow site transformers are Centre Tap Earth hence the need to earth the centre tap so the max voltage to earth seen is 55v from either live,
or are you poking fun as Ricicles senior moment as he should have said winding?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top