Wiring a relay to protect a programmer help.

Hi. Thanks for the advice and link.

There is no spare place in the receiver to install this. Unless it is really small but I cannot find the dimensions of it.

There is nothing about it specs I can find online. It just calls it the receiver.

Sorry I cannot find any specs on the v3+ receiver.
 
I can see from searching that this is a common issue with Tado receivers - only about a 6A contact so probably not enough.
A lot of programmers are only 3A, so why would a relay be needed? Heating systems are fuse rated with 3A too so I’m slightly confused.
It is the Tado doing the switching
It’s a Y plan, so should be Tado - MV - Pump and boiler switch live, so still confused as to why it would be the pump drawing too much load
 
A lot of programmers are only 3A, so why would a relay be needed? Heating systems are fuse rated with 3A too so I’m slightly confused.

It’s a Y plan, so should be Tado - MV - Pump and boiler switch live, so still confused as to why it would be the pump drawing too much load
Read what hte TADO CS said, a pump can give a large load/high inrush current on switch on.
It's a common problem according to Google.

I build electrical control panels for much much larger pump, we sometimes have to increase/swap the MCB for a bigger one/different type than what was expected.
 
If the TADO contacts are rated 6A and they fail so frequently, I’d use a 30A relay.

You should also consider whether the pump is on its way out. Maybe this will save the TADO, but then the pump will fail completely in 6 months time, and the replacement pump will not need it.
 
You can find a small enclosure to fit the relay in that will easily be able to be fitted in the airing cupboard.
 
Read what hte TADO CS said, a pump can give a large load/high inrush current on switch on.
It's a common problem according to Google.
I did read it. What I also saw was a com to no on heating, not on dhw.
I build electrical control panels for much much larger pump, we sometimes have to increase/swap the MCB for a bigger one/different type than what was expected.
Probably understand it better than me then. I’m only a gas engineer with limited heating wiring/electrical knowledge
 