Worcester Heatslave - heating issue

Joined
17 Nov 2023
Messages
9
Reaction score
1
Country
United Kingdom
Hello... I'd be grateful for opinions on what may be causing the following symptoms on my Heatslave combi boiler (oil). When I turn the heating on, hot water will initially circulate around the system normally, but will eventually stop circulating and the radiators will cool down - but it does appear that the CH pump is still running and is quite hot. If I open a hot tap, I can hear a relay click and the boiler will give hot water to the tap AND it will also start circulating hot water around the radiators. I'd be grateful for your advice. Many thanks!
 
Sponsored Links
Thanks for your replies guys. Just a bit of a follow-up. I forgot that I had previously put the diverter valve manual switch across (which I presume gives both hot water and heating?). I think the heating stopped last winter so I did that to get it going again - boiler was hardly used since spring then. So, I should probably start again with my request for help...

After a bit more looking today - it appears that the rads will only heat up when the diverter manual switch is pulled across. So, I'm guessing there's a valve or motor issue there.

However, the pump on the boiler will not come on when the heating is turned on. It only comes on when the hot water is on/active and the burner comes on to heat the water - which is either when it needs to get up to temperature or when the hot water tap is opened. Once the burner stops, the pump stops (I'm gauging this by feeling the pump vibrations, and also feeling the hot water entering the rads). I don't even know if the pump should be running with the hot water - but it doesn't make sense that it should run constantly when the burner is, but no hot water taps open (just guessing here).

Is there something obvious wrong in that the water pump is not being called in when the heating is on? The pump is not activated when the hot water is off and the burner is running with heating on.

Hope the above makes some sort of sense.

Thank you!

P.S. seems similar to this post: https://www.diynot.com/diy/threads/worcester-15-19-ch-comes-on-when-only-dhw-should-be-on.127605/
 
Sponsored Links
I put a new power head on mine......the Honeywell seems to be best but I have used the Toostation
equivalent.
John
 
Thanks everyone. I'm assuming the actuator calls the pump in then?

It's a Honeywell V4044F1109 with 5 wires.

Is your recommendation only to change the actuator, and not the actual valve? The valve seems to be switching ok with the synchron manual switch (if that helps any).

Thanks again!
 
The head/the actuator/the top section is the common point of failure, they wear out - microswitches fail, the motor fails, the mechanism wears out. The actual water valve below it, tend to be much more robust, as well as more difficult to swap - so the usual advice is to just change the actuator.

They are such a common point of failure, and so cheap, so easily swapped - it's well worth it to keep a spare one to hand, ready to fit.
 
Last edited:
Thanks guys - much appreciated. With regards to the head, do I need to match up the exact model, or can I fit other model numbers that have the the correct mountings and have 5 wires? There appears to be a big difference in pricing between this exact model and others that appear to be similar. I appreciate some wire joining may be necessary, so some don't come with a connector plug. I appreciate that some of these other models may have different micro switches etc too. I'd rather not learn the hard way - but I'll gladly save a few quid if I can.
 
Thanks guys - much appreciated. With regards to the head, do I need to match up the exact model, or can I fit other model numbers that have the the correct mountings and have 5 wires? There appears to be a big difference in pricing between this exact model and others that appear to be similar. I appreciate some wire joining may be necessary, so some don't come with a connector plug. I appreciate that some of these other models may have different micro switches etc too. I'd rather not learn the hard way - but I'll gladly save a few quid if I can.

Fit the same model head, then it is certain to work.
 
The head contains a microswitch which brings on the boiler with pump when the valve is moved to a position.

But it is most likely to be only a failed motor. Just changing that is likely to be the easiest and cheapest option. Often called Synchron motor as that is the brand name of a well known manufacturer.

Often available for around £10.
 