Landing wont turn off unless it is turned off downstairs.

Joined
11 Sep 2004
Messages
31
Reaction score
0
Country
United Kingdom
A while back i installed new light switches all over the house. Everything works fine except the hall/landing light.. EWhen i turn on the light at the top of the stairs from down stairs i can only turn it off downstairs. If it is turned off downstairs i can turn it off and on from the upstairs switch.

In each light fitting i have a yellow/green secured to the metal box fitting and 2 other cables with a red and a black in each cable...The double light switch upstairs also operates the bathroom light.

Can anyone shed any light on my problem. Cheers
 
Sponsored Links
Yup. Two-way switching works by providing alternative paths for the current - what you've done is wire the two switches in what seems to be a parallel arrangement.

Read the post at the top of this forum, entitled 'For reference'. There are plenty of examples there. If you can't identify and fix your problem from those then at least you might be able to ask more specific questions later, which will help people sort out your problem.
 
since it only went wrong after you changed the switches, you have put the wires in the wrong place.

as you do not mention which colour goes where i can only suggest the following

remove downstairs switch, copy the switch connections for the landing light, the remaining 2 wires (not earth) should go in L1 & L2

you can see what i mean by looking in the sticky for refernce posts in UK electrics
 
wow that was quick..

will try out your suggestions.

Thanks
 
Sponsored Links
ok here is how the wiring stands.

downstairs..

light for bottom of the stairs. 1..black
c..red works fine
2.. blank

bot switch for landing light 1.. blank
c..red
2.. black


there is a red wire bridging both c wire connections
----------------------------------------------------------

upstairs switchs

bathroom...1..black
c..red works fine
2..blank

landing light switch 1.red
c.red
2.black

hope this helps guys
 
OK, here we go..... i will do a pic aswell.

Downstairs, hall, leave as is, with red link rom C to C.

should be 2 other cables left, these go to L1 and L2 of upstairs switch.

On the upstairs switch, leave bathroom as is. C to a red in its own sheath. L1 and L2 to the the other two cables (either way)

Hope it helps...i will try to do a pic.
 
landing.gif


Circles represent the cable sheaths (outer cable part).

The red on its own may have a disused black (possibly chopped off), this isnt used.

Hope this works, let us know if not!
 
Sorted.. Followed your diagram and it's now working fine. No more having to run downstairs to turn the landing light off.

Cheers Lectrician :p
 
Lectrician said:
landing.gif


Circles represent the cable sheaths (outer cable part).

The red on its own may have a disused black (possibly chopped off), this isnt used.

Hope this works, let us know if not!

hello i have the same problem can you please show me the same diagram
 
As everyone wiring is different it may be better if you tell us how yours is wired, also start a new topic as this one is 2+ years old.
 