H
holmslaw
High Ze.
Max Zs for a B32 is 1.44 ohms. Max Zs for a B6 is 7.67 ohms, no RCD for utility room and lighting circuits?
Arguably the Zs for a circuit protected by a 30mA RCD can be up to 1667 ohms. Why the differing RCD times?
Not sure if it's required on this form (mine are different) but do you not need to put in R2 values for the main equipotential bonding conductors?
Looks very neat!![]()
Good luck
Good point. It needs to be tested in isolation so same figure for each final circuit being protected by it.
r2 value for way 8 upstairs sockets seems high. I would expect around 1.08ohms.
Poor connections at socket outlets?
How do you get a Zs reading less than Ze?
Eric
I stand corrected, thanks for pointing that out. In defence, I was instructed to put the value in the R2 column. 'Gas equipotential bonding conductor' etc went in the Circuit designation column, leaving a few rows spacing from the numbered circuits.
I can't quite make out the figure. Is it 1.08 or 1.82 or 1.92??
Gary, the preference is to test RCDs at an appropriate point(s) in the circuit. I seem to recall ERA (or someone) mentioning this in an RCD paper. Testing on the terminals can give odd/incorrect readings and with some RCBOs very odd.
1.92
1.92
Wow. I wonder if the reading was measured from the front via an adaptor. Marbo sockets in particular are very flaky if measured this way. MK always rock solid though and Crabtree always good.
GN3: The test is made on the load side of the RCD between the line conductor of the protected circuit and the associated cpc. The load should be disconnected during the test.
Couldn't that mean at the load terminals of the RCD with the outgoing circuit disconnected?
1.92
r2? I would hope it was end-to-end resistance of the cpc at the consumer unit!
I always thought that the entered figures on certs where it says Max Permissable Figures are those directly from BS7671 i.e. uncorrected. Maybe I have picked this up from the NICEIC?These are design figures and represent the absolute maximum figures given the test conditions referenced in BS7671. BS7671 makes this clear at the foot of the Zs tables in Chap. 41. As such, the maximum figure entered on the sheet should be the maximum permissable figure taking into account ambient and conductor operating temperatures and it is against this value that the measured value is compared.
can I delete that one...miles away...too many thnigs at once...
The corrected figures in the OSG/GN3 are for a copper conductor with an operating temperature of 70deg C measured at 10 deg C, outside those figures further correction is required.