And there would always be the option to find a logical place to split the ring and turn it into two radials. (You could even leave the cpc as a ring, as per 543.7.2.1(ii)(c), if you want to retain the resilience it offers.)
However for a radial type A2 on 2.5 it must be fused at 20A or less.
4 pages of discussion over what is laid down in simple terms with drawings in appendix 15......come on fellas!
433.2.2 specifically says
433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )
please note the highlighted section..
would you consider a single or double socket an "outlet for connection of current-using equipment"?
your follow on argument will likely be that the plugs all contain fuses...
but it doesn't specify that and that's not entirely true either..
there are special "red" plugs that contain no fuse.. while these are not in general use they are fitted to some protable machines that have large current demands for a short duration, such as portable x-ray machines..
while the example of the hand dryers would satisfy 433.2.2 in some way if the faut current requirements were met, this is only because they have permanent connections and not outlets...
to mean as a branch not at end of line.outlets for connection of current-using equipment
can you have just a single or double socket wired in 2.5mm² from a 32A breaker?
and I am afraid many electricians don't consider that they just do it that way because they have always done it that way.(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )
Yes but maximum of 3 meters in length.
434.2.1 The regulations in Regulation 434.2 shall not be applied to installations situated in locations presenting a fire risk or risk of explosion and or where the requirements for special installations and locations specify different conditions. Amended July 2008
Except where Regulation 434.2.2 or 434.3 applies, a device for protection against fault current may be installed other than as specified in Regulation 434.2. under the following conditions:
The part of the conductor between the point of reduction of cross-sectional area or other change and the position of
the protective device shall:
(i) not exceed 3 m in length, and
(ii) be installed in such a manner as to reduce the risk of fault to a minimum, and
NOTE: This condition may be obtained. for example, by reinforcing the protection of the wiring against external influences
(iii) be installed in such a manner as to reduce to a minimum the risk of fire or danger to persons.
Oh dear back to 3 meter rule I see!!!!!
Yes there are some special places where it is allowed to use no protection but this hardly applies to a house.
But not at all for double sockets, as there is a branch before the protective device (fuse plug).Oh dear back to 3 meter rule I see!!!!!
... I would like to change my answer from a blanket yes to yes up to 3m (single), and no (double).ColJack said:can you have just a single or double socket wired in 2.5mm² from a 32A breaker?