Hey guys, I have a new install and I have racked my brains trying to decided how this can be, so if anyone has any ideas then please add your input.
New House.
Ring main at fuseboard all disconnected.
Insulation Resistance L-L 0.0Meg Ohms, N-N 0.0Meg Ohms, E-E 0.0Meg Ohms.
Continuity Resistance L-L 0.97Ohms, N-N 0.97Ohms, E-E 0.74Ohms.
As you can see the earth continuity is not what I would expect, and would expect around 1.6Ohms.
Now leaving the ring disconnected at the fuseboard and going to mid point in the ring and disconnecting all legs I find the following,
L-L Clear, N-N Clear, E-E 0.0Meg Ohms ??
How can this be ? with ring broken each end.
L-E on one leg 299Meg Ohms, L-E on other leg 54Meg Ohms.
It seems like the earth is bridged somewhere but it's not as L-L, N-N are fine. Although a different Meg Ohm reading appears on each side at this point.
Another odd thing is it's a TT system and with the L-L,N-N,E-E all disconnected at fuseboard, then megger between each one leg of ring earth and earth bar which only has spike connected I get 0.0Meg Ohms ?
If it was not for the weird earth continuity readings on Live and Neutral all seems ok, Rcd's hold no tripping etc.
It is a new build with walls freshly painted and typical damp from plaster/render, and considering you a have fixed lug on each outlet could this give the earth continuity lower than the L & N.
Has anyone else had this and found why.
Thanks for any help.
New House.