Prv's aren't just found in boilers therefore their discharge can't be broken down into it must be this for this and this for that,why would a prv's discharge need to be in metal on say a cold water inlet group.
If you've got a boiler prv discharging steam then you've got issueswith multiple failures prior to the point of discharge.
The differnwve between the two valves described is simple a TPRV is a primary safety device which is designed specifically to relieve pre boiling water therefore it relief pipework should be able to with stand this.
A PRV on a boiler is a 3rd line safety device whose primary function is to allow discharge over 3bar,it's no way operated by temperature an therefore it's pipework doesn't need to be designe to allow for this.
If this operates with water close to boiling point it will be because overheat stat,thermistors,expansion vessel etc are all at fault.
Leave the pipe as it is...at worst it's not to manufacturers instructions.if BG took it on contract like that it's their fault for not doing a better initial inspection,certainly the rules for boiler PRV's haven't changed in years.