As the VD figures in the tables are the same for three and four core cables, is it that the neutral is considered as if the current were the same as the line - just in case?
I think I would have guessed the opposite! If they're quoting the same VD for 4-core as for 3-core, I would have thought that would mean that they were assuming that the VD due to the neutral (hence the neutral current) was zero (i.e. perfectly balanced phases).As the VD figures in the tables are the same for three and four core cables, is it that the neutral is considered as if the current were the same as the line - just in case?
For a given run, to calculate the voltage drop (in mV) the tabulated value of voltage drop per ampere per metre for the cable concerned has to be multiplied by the length of the run in metres and by the current the cable is intended to carry, namely, the design current of the circuit (lb) in amperes. For three-phase circuits the tabulated mV/A/m values relate to the line voltage and balanced conditions have been assumed.
Ah, it's reassuring to see that I occasionally get something rightFrom the regs:
... For three-phase circuits the tabulated mV/A/m values relate to the line voltage and balanced conditions have been assumed.
Then why are the values so similar to two-core single phase?I think I would have guessed the opposite! If they're quoting the same VD for 4-core as for 3-core, I would have thought that would mean that they were assuming that the VD due to the neutral (hence the neutral current) was zero (i.e. perfectly balanced phases).As the VD figures in the tables are the same for three and four core cables, is it that the neutral is considered as if the current were the same as the line - just in case?
One of my uncertainties is exactly what they mean by 'voltage drop' in the 3-phase situation - I'll have a read of the text to see if it clarifies.Then why are the values so similar to two-core single phase?I think I would have guessed the opposite! If they're quoting the same VD for 4-core as for 3-core, I would have thought that would mean that they were assuming that the VD due to the neutral (hence the neutral current) was zero (i.e. perfectly balanced phases).
Yes, thereabouts.I would expect it to be about 86.6% of the VD for a 2-core single-phase situation (how does that compare with the Tables - I don't have them to hand?).
Aren't the figures in the VD tables (in BGB) already doubled, i.e. for both conductors.My reasoning: Consider a cable of length L with a voltage drop of D mV/A/m per conductor (e.g. 0.75 mV/A/m for 25mm²). For a 2-core single-phase situation, with current I flowing (in both L and N), the voltage drop will be 2*D*I*L mV.
That sounds promising ... maybe I'm on the right track, then.Yes, thereabouts.I would expect it to be about 86.6% of the VD for a 2-core single-phase situation (how does that compare with the Tables - I don't have them to hand?).
Yes, the figures (for 2-core) in the table are already doubled - but, as you've quoted me as saying, my 'D' was for a single conductor (i.e. half of the ('doubled') figures in the BGB Tables - e.g. the example I quoted: D=0.75 for 25mm², as compared with 1.5 in the BGB table).Aren't the figures in the VD tables (in BGB) already doubled, i.e. for both conductors. ... Hence my query as to why one-phase and three-phase are similar (86%) and not roughly half (43%)My reasoning: Consider a cable of length L with a voltage drop of D mV/A/m per conductor (e.g. 0.75 mV/A/m for 25mm²). For a 2-core single-phase situation, with current I flowing (in both L and N), the voltage drop will be 2*D*I*L mV.
Not entirely.Yes, the figures (for 2-core) in the table are already doubled - but, as you've quoted me as saying, my 'D' was for a single conductor (i.e. half of the ('doubled') figures in the BGB Tables - e.g. the example I quoted: D=0.75 for 25mm², as compared with 1.5 in the BGB table).
Does that clarify?
No. I wish I were with you and a blackboard - it would be so much easierNot entirely. As the figures for three phase are 86% of single phase are they not also including the neutral? If not, shouldn't they be 43% of the single phase?Yes, the figures (for 2-core) in the table are already doubled - but, as you've quoted me as saying, my 'D' was for a single conductor (i.e. half of the ('doubled') figures in the BGB Tables - e.g. the example I quoted: D=0.75 for 25mm², as compared with 1.5 in the BGB table). Does that clarify?
You got it! I guess you did not notice, about 3 posts back, when I wrote (with a typo of a suiperfluous "√",which may have confused you!):Ah. penny's dropped. 86.6 = (√3)/2 Thanks.
(D*I*L*√3) / (2*D*I*L)
= (√3 √ / 2) = 0.866 (or 86.6% if you prefer)
should have been
= (√3 / 2) = 0.866
It is a rather odd display/printout we've been shown - I suspect it is only part of the whole. The software clearly knows about a lot of things it hasn't displayed in what we've been shown, since it's somehow calculated Zs (hence it must know about the CPC and 'Ze'), disconnection time (hence it must know about the OPD) etc. etc. There are all sorts of aspects of what we've been shown that I don't fully understand. I wonder if Lectrician might perhaps be able to provide us with a link to a manual for this software?One thing I have noticed in the results picture in the original post is - that while it doesn't state the length of the cable or VD figure (you'd think it would) it states that the volt drop is 8.45V and the maximum length for volt drop is 204.1m
Yes, that's interesting - but are we really sure it was assuming single phase? - I'm not sure what a 'cable makeup' of "1 x 1 x 4c" means, although I suspect that '4c' probably means 4-core - hardly 'single phase'. The absence of anything under the 'Sep CPC size' field might suggest that it is assuming that one of the 4 cores is a CPC, hence no neutral! However, the 'Earth Fault Current" has clearly been calculated from the Zs on the assumption of 230V, so I don't know.For 230V single phase, which was being used, this is the correct proportion - 8.45 / 150 x 204.1 = 11.5V.
The nearest to a bell that rings is that 0.805 mV/A/m is close to being half of the 1.65 mV/A/m figure which ricicle suggested should be used when one knows nothing about PF. If it were 1.65 mV/A/m for single-phase L+N, that would be 0.825 mV/A/m for each of the two conductors. If the software was actually thinking of balanced 3-phase (70A in each phase, zero in neutral {or no neutral!}) then, for a 150m run, the VD along each phase conductor (i.e. the VD in terms of phase-neutral voltage) would be calculated as 0.825 x 70 x 150 / 1000 = 8.66V, not too far off the software’s 8.45V. If ricicle's figure had been 1.61, it would have been 'spot on'.The machine would appear to be using a VD figure of 0.805mV/A/m - 1.5 x 8.45 / 15.75 ... I don't know what this proves, except that it is the VD figure which is going wrong, but does it ring any bells?