Ah, I see - so one doesn't need to undertake tests if one has results of tests undertaken by someone else (probably 'a stranger')?There should be another schedule with the necessary information.
I did?You know that's not what I meant.![]()
That's obviously different. One obviously should not really trust a stranger's word, but if one is going to leave the floorboards and walls etc. intact, then the stranger's word is probably more likely to be correct than a wild guess as to the installation method!How are you going to check the installation method? Lift the floorboard, knock down a wall or believe 'C' or '103' on a stranger's schedule?
If the cable installation method allows, you could change the MCB on the heating circuit to 16A and do as you have suggested.
That is one socket and FCU.
What power is your microwave, and how long did you have it on for? A 6A MCB will allow about 8.7A (about 2,000W) to flow for an hour, and appreciably greater currents than that to flow for shorter periods of time, without tripping. On a sockets circuit (when you don't know what will get plugged in) the MCB is just there to protect the cable (so any size less than the current carrying capacity of the cable is fine), and one could't size it according to the (unknown) load, even if one wanted to.So before I changed the MCB to the 16A one from the 6A one, I plugged the microwave in and and to my shock everything worked fine, the 6A MCB did not trip, and everything seemed great. Ive now changed the MCB to a 16A as recommend, but i'm now confused, if the 6A one was fine and not tripping, I should be using that really? I thought you should always use the lowest MCB/fuse you can get away with?
That wouldn't even trip a 2A MCB.Thanks. Its a 800w Microwave, had it on for about 5 min warming up some food.
Well, if you were absolutely certainly that you (or anyone else) would never want to plug in anything other than (or in addition to) the microwave, then a 6A MCB would be adequate. However, a 16A MCB provides ample protection to the cable so that 'more/btter protection' would not make it any safer.The circuit only has the boiler (3A FCU) and my new single socket, which will only ever have the microwave plugged in. Given that, would the 6A MCB protect the cable etc better and therefore be safer?
Thanks. Its a 800w Microwave, had it on for about 5 min warming up some food. The circuit only has the boiler (3A FCU) and my new single socket, which will only ever have the microwave plugged in. Given that, would the 6A MCB protect the cable etc better and therefore be safer?
Nope. Your 16A MCB is good for up to about 3,680W. Even a 6A one would be OK up to about 1,380W.Thanks. Will 1200w make a difference to my setup/MCB etc?