I hope it is only MY logic that is failing... ...and that YOU can figure it out!
This happens to be in Cyprus, but it could just as well be the UK or elsewhere.
Immersion heater (IH) connected to Neutral-Earth fault.
I installed a new one (Backer 314C, 3kW), ran for an hour then RCD tripped and would not re-engage. The previous one ran for 2 weeks then the RCD became un-engageable.
The RCD is a 300mA one protecting the whole property (detached villa).
When switched on, the RCD trips (usually immediately, but sometimes taking a few seconds).
If I bypass the original wiring and connect the IH to a 13A socket running off a different circuit from a different subDB, protected by a 30mA RCBO, that RCBO trips.
That happens even if the live is disconnected at the IH, and all 3 phases are disconnected at their isolators (there is a main DB and many subDBs), and all neutrals in the main DB are disconnected except the supply and the one serving the affected DB. That is: there is no load anywhere in the property (hence no means therein of raising the potential of the neutral), and the only connections running from the meter box to the 30mA RCBO are neutral and earth.
(the MCBs alongside the 30mA RCBO are all off)
Further info:
The system is TT or TN-S or TN-C-S (uncertain because there is an earth rod in the ground in the meter box, and the SWA supply is 4-core (no CPC core) and I don't know how the armour is connected upstream). Other villas in the development have similar supplies but don't have this N-E issue.
There is 1.6V across N-E at the IH (less in the meter box), presumably arising from loads upstream in other villas. For 1.6V to trip a 30mA RCBO, a resistance/impedance of 53 Ohm or less is needed. I can test the resistance of the IH N-E only with a basic multimeter, not a Megger; I get open circuit, ie. inconclusive. But this IH is only a day old. It seems soo unlikely that it would develop a N-E fault so quickly.
(other IH resistances: L-E infinite, L-N 19 Ohm (correct))
Last three thoughts:
In writing this, I realize I have not disconnected neutrals in the nearest DB. Although all phases are isolated (and there is no micro-generation on-site), I must disconnect them to ensure a low N-E resistance (<~50 Ohm) is not lurking there.
Other folks before me have been on-site and not found an explanation. They always end-up replacing the IH, and always the fault recurs soon. There have been 7 IHs in the last 3 months, no doubt bought from different stores.
I am loathe to replace it yet again without understanding the real problem!
If pushed, I would say:
- the cabling is OK
- something (specific to this one villa) is causing the IHs to fail prematurely. The only anomaly I have seen is mains voltage sometimes being 245V (the IHs are rated for 200-240V). Most of the times that I have measured, the voltage across the supply to the IH terminals has been 237V (off-load) and 227V (on-load), ie. within spec.
Any clues?
Thanks very much, for reading my post at the very least.
Further info:
- the cabling is OK
Any clues?