NOT if it is protected against fault current.
433.2.2 ... and fulfils at least ONE of the following conditions:
(i) ...
(ii) ...
READ IT.
(i) ...
(ii) ...
READ IT.
So what are you doing when you start reading a reg, see that it says something along the lines of "A or B is OK", and decide to completely ignore A and tell people that B is the only way to comply?So you can't explain you're stance. Well I'll explain it for you, you start reading a reg and as soon as you find a sentence that you think suits what you wanted to do, you stop reading.
433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor. or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) Its length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum,
and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons (see also Regulation 434.2.1).
Please note amendment 2 or 3 may have changed the wording slightly. 433.2.2 was an "or" but 434.2.1 is an "and" on my copy. May be this has now changed as I don't have amendment 2 or 3. However in this case it really does not matter as the FCU is well within the 3 meters and even if it were not there seems to be some uncertainty as to if this applies to a ring final.434.2.1 The regulations in Regulation 434.2 shall not be applied to installations situated in locations presenting a fire risk or risk of explosionandor where the requirements for special installations and locations specify different conditions. Amended July 2008
Except where Regulation 434.2.2 or 434.3 applies, a device for protection against fault current may be installed other than as specified in Regulation 434.2. under the following conditions:
The part of the conductor between the point of reduction of cross-sectional area or other change and the position of the protective device shall:
(i) not exceed 3 m in length, and
(ii) be installed in such a manner as to reduce the risk of fault to a minimum, and
(iii) be installed in such a manner as to reduce to a minimum the risk of fire or danger to persons.
NOTE: This condition may be obtained. for example, by reinforcing the protection of the wiring against external influences
Try:433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor if the part of the run between the point where a change occurs (in cross-sectional area, method of installation, type of cable or conductor. or in environmental conditions) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfils at least one of the following conditions:
If you had you would see that the entire first sentence you quoted has gone. 434.2.1 begins "Except where Regulation 434.2.2 or 434.3 applies...."Please note amendment 2 or 3 may have changed the wording slightly. 433.2.2 was an "or" but 434.2.1 is an "and" on my copy. May be this has now changed as I don't have amendment 2 or 3.
The circuit topology is irrelevant.However in this case it really does not matter as the FCU is well within the 3 meters and even if it were not there seems to be some uncertainty as to if this applies to a ring final.
For you maybe, some of us want to have a constructive forum environment not just pointless insulting. Makes you look worse tbh.Winding up BAS is a forum pastime, she's so easy.
You aren't winding me up.Winding up BAS is a forum pastime, she's so easy.
Either way he shouldn't be here.I have explained my stance but you are ignoring it or incapable of understanding.
Well, why don't you explain, you could cause me maximum embarrassment and maximum kudos for yourself.
Not strictly true - that is why you are required by design to ensure that a small overload of long duration can't occur as the cable could then be unprotected.near every other circuit is protected at the origin and what ever you do you can't over load it without a protective device disconnecting the supply