One has to be careful with freezers, volt drop is a problem, the freezer can only start if there is no pressure in the system, there is a start delay to allow the pressure to drop before it tries to start, and also an overload which should the motor stall will switch off the motor and once cooled try again, this overload has a limited life, and if the freezer has to try to start multi times then the overload will burn out. Volt drop can also cause the freezer not to start and have to re-try, for this reason nearly every freezer has a warning not to use it on an extension lead as extra fuses means more volt drop.
This has been compounded as of late, due to solar panels, our voltage is officially 230 volt, but for many years it was 240 volt, and in real terms the main transformers never had their tapping changed to drop to the harmonised 230 volt, however solar panels have to be designed to auto switch off should the voltage go too high or too low, it's all part of the safety system, so if the tapping on the transformer is too high, the solar panels auto shut down, so now the DNO have to drop the voltage to the correct 230 volt.
This means that freezers which have for years worked in a garage or shed, fail due to low voltage, it is only one small part which needs changing once they fail, but the domestic refrigeration trade tends to be van based and it costs around £60 for a call out even if the part is cheap. Modern freezers are now starting to use three phase motors and inverter drives which removes this problem, but as yet only the more expensive models.
So to use a freezer in a garage or shed, one has to be careful that there is not an excessive volt drop, old type freezer has a load of around 10 amp on start, so the loop impedance (L - N) needs to be 1.87Ω or less so at 10A the voltage does not drop more than 11.5 volts which is maximum allowed, in general if old fluorescent lamps work OK then freezer also OK. New fluorescent lamps now also use inverters so don't have a problem with volt drop.