Let me first list the set-up we have:
The 2 main problems we have are:
1. Struggle to get good heating to all radiators despite balancing
2. Can't have hot water and heating on at same time as hot water cylinder ends up getting priority (next to boiler) and the heating system suffers
I have tried to detail both of the above in the two headings that follow.
Heating problem:
The boiler stopped working a few days after the power-flush (keeps overheating and switching off then restarting). The plumber sent by the home emergency insurance said (off the record) that the boiler's internal pump and the external pump were not enough for our house and between them, they were causing circulation problems (i assume that they run a different speeds so this could be a reason). He advised us to add an auto air vent (which we have done now), and he recommended that I change the boiler to a heat only boiler (ecoTec plus 438) and add a bigger pump (Grundfos 25-80).
Questions that I have:
1. Is this a good recommendation?
2. Can we get away with changing just the pump for a bigger one?
3. I understand the wiring diagrams for boilers (we have an S plan system). Is it straightforward to fit the new boiler (i.e. connect flow, gas, return, power from relay, switched live back to relay) and then to configure it?
Simultaneous heating and hot water problem:
The plumber mentioned above said that the cylinder thermostat should switch off the zone valve when the temperature of the water in the cylinder reached the target temperature. However, I have never known the zone valve to switch off (not checked the zone valve's manual level, but I am assuming) so the boiler is constantly heating the water; the water temperature does get hotter if we turn up the cylinder thermostat. Does this indicate:
1. The plumber is mistaken?
2. The zone-valve switch-off function of the thermostat is faulty?
3. The thermostat is wired incorrectly?
Thanks in advance
- Vaillant ecoTec Plus 637 system boiler
- Zilmet unvented hot water cylinder with external expansion vessel
- 1 zone valve for Central Heating
- 1 zone valve for hot water cylinder
- 1 Grundfos 15-50/60 circulation pump (on flow pipe from boiler)
- 16 radiators (including towel radiators and hot water cylinder)
- 3 floor house: 4 bedrooms + 3 bathrooms (with towel radiators in each) + outbuilding (2 radiators)
- Powerflushed the system out extensively over the weekend in both directions and flushed the boiler as well (don't think the system was ever flushed before)
Heating problem:
Thanks in advance