Is my differential bypass valve stuck?
18 Jun 2016
Our radiators on the bottom floor are not getting hot, I've been having a look on the weekend and came across the bypass valve on my S Plan, three zone (inc hot water) system.
When the heating system is fully on, the pipes to and from the bypass valve are very hot.
It would look to me that the valve is stuck open and does not close. I have taken pictures of the valve early morning when the pipes are stone cold.
What is the best method to loosen the valve and get it working again?
Thank you.
Is the valve the correct way round - arrow points from flow to return?
What number is it set to?
Hello,
The flow and return are correct based on the pump.
There is no number on the valve, does not seems it can be turned.
Reading online mentions the valve would adjust itself based on flow.
you need to take the clear cover off it before you can turn it.
1st, turn on only the zone thats not been heating, make sure other heat zone and HW are off. then check the zone valve to that zone has actually motored open, if it has, remove the clear cover from BYpass and turn the handle clock wise to close it down and see if any heat pushes to that part of the system.
Hello,
I've tried to take over the clear cover, but it does not come off.
I looked online as we have a Kingspan system and it mentions a automatic bypass valve, so I'm thinking that it adjusts itself?
I have attached the manufacturer's instructions.
The valve is automatic in the sense that it opens and closes automatically depending on the water pressure. The actual pressure at which it opens will depend on the installation; the valve has to be adjusted so it opens at the correct pressure.
  • ARV22.pdf
Thanks all,
I will need some sort of mirror to take the reading as its on the other side.
However, from cold, I will ensure everything is off and the valve is in the closed position. I will then turn on both zones and HW and let the system reach temperature. I will then turn the valve slowly counter-clockwise until the valve begins to open, I can monitor this by the temp. At this stage turn the knob clockwise half a turn to complete the setting process.
Should I be using the above method, or do I need to read the boiler manual and understand the pump speed (which is set to high, I have microbore) to then work out the right settings.
I have a Potterton SL 15 with Kingspan TT210PT4 with a Grundfos UPS025-60 Pump set on Speed 3.
Can you be a bit more specific as there are several SL 15 boilers. The GC number (on manual or boiler data plate) would help
The pump PN number (on front data plate) would help identify the correct pump curves.
How old is the system?
The system is five years old.
For the pump I have the following:
Grundfos
UPS025-60 130
P/N: 97781518
PC: 1239KIN
Thank you.
Thanks for Boiler and pump info. I can't find any data on the pump; it's not listed in any Grundfos catalogues. I suspect it's a special for Kingspan - the KIN in the PC number. which is the date of production (2012 week 39), is the clue. But, based on the standard UPS 25-60, a setting of about 4 should be about right. If you find the exit pipe, i.e the one connected to the return, is hot a lot of the time turn the valve to a higher number. The valve only needs to be open when the boiler is running at minimum output.
