Dead boiler Vailant Ecotec Pro 28
So if you observe the led panel using the i button what sequence do you get please. Do you have the install instructions? It lists all the S codes to explain their meaning.
S.30 code
Room thermostat is blocking heating mode
I have a Hive wireless stat connected to the boiler
Post a picture of the wiring into the boiler please. If you bridge 3&4 does the boiler fire up, if not measure the voltage on both with a multimeter, one probe on the negative in, the the other on either 3 or 4, what doe you get? You need to see 240 V on at least one of them
Even with hive disconnected at the boiler and boiler reset it still has a S.30 code when using the buttons to view
You should have 240v not 24 on those terminals. Don't like the flash on the pcb though
Definitely getting 24v between neutral & RT terminal not 240v
sorry flash may have been incorrect. Poss. The resettable fuses .
Which connection are your external controls connected to?
So if you disconnect these wires from the hive and jumper the two pins on the 24v rt connections the boiler doesnt fire up?
If I fit the link wire between 24 & RT something starts to run for about ten seconds but it’s not the boiler firing. But then then the boiler shuts down