Hi All
This is my first post here. Have been using this forum for a while but just joined. I have recently changed a radiator in toilet downstairs with a column type and it didn’t warm up properly. I thought I would balance the whole system to get it right. Searched the interweb a lot but many of things people talk about doesn’t work for me. I have studied mechanical engineer and understand some of it. This is the story:
The house is 3 years old in 3 stories. Combi boiler is ideal logic+ esp1 35. The boiler is downstairs, auto bypass valve and motorised zone valves are first floor. Zone one is ground floor and zone two is 1st and 2nd floor. Each zone has a standard danfus room thermostat. An outdoor sensors is wired to the boiler. There is no expansion vessel anywhere in the system other than the one inside boiler.
In an attempt to balance, I noticed:
1- auto bypass valve stuck open. Replaced it.
2- 5 out of 13 radiators has TRV on return. Swapped TRV and lock-shield valve on those.
I closed valves on 11 radiators and only left two radiators with double lock shield on. Although they are fully open, I have to set auto-bypass to 6 (around 0.6bar) to prevent any bypass. ABV is 1.5m higher than the pump.
Then I found the order of radiators in terms of distance to boiler and started balancing. I have to be extremely accurate with lockshield valves to get anything more than 5’C temperature difference(I use twin input thermometer). This applies to the radiators furthest from the boiler with two unrestricted flow on twin lockshield radiators.
even different between flow and return just below the boiler hardly goes above 8’C.
Even if I try to restrict the flow using flow or retun valves beneath the boiler the delta T will not go beyond 11’C. In fact boiler ramps up the flame and fan speed.
instruction manual does not mention how to adjust the pump speed. It is controlled by boiler and the only setting I could find was to set minimum pump power to 70%. It does mention temp drop over rads should be around 20’C.
The only reason I can think of is that the boiler is unnecessarily running pump at high flow and kicks the flame in to keep delta low.
All lockshield valves used to set fully open before I start and now I set them at absolute lowest flow which they will shut with slightest knock! Maybe 1/16 of a turn. Even if I could balance them, two rads with unrestricted flow will increase the return temp and boiler will not work at condensing point.
would you guys help me to understand what I am missing here?
thanks
thanks