I would like to know if it's advisable to have the 32A RCBO fitted
How many amps does a 9.5kW shower draw?
Think for a sec why I maybe posted this topic in the first place. MMmmmm, could it be that I'm seeking the opinions of pros in this field? What I'm not getting into is answering loaded questions like yours.How many amps does a 9.5kW shower draw?
Mate...why dont you give him some advice instead of trying to be clever....(not being funny at all)Nobody, no matter how much of a "pro" they are, can have an "opinion" which contradicts Ohm's Law.
And it's not a "loaded question".
What that table is showing is the maximum current carrying capacity of a cable under various conditions, using Ebee's figures; basically any figure below 40A that on the chart should be avoided so that'll be the red, the amber may just be suitable for the heater if you have 230V but would not be correctly protected by a 40A MCB/RCBO and the green is fine.Hi all
Thanks for further replies. Yes, he advised the tripping was due to poor installation of the isolator switch. Cables partially burnt out due to poor connections, not all of the live cores terminated.
The shower manufacturer doesn't recommend 6mm with 32A coupled to a 9.5kW model. Indeed, they state it's best to use a minimum of 10mm if the cable is likely to run in any situation that isn't ideal.
However they do state 'The current carrying capacity of the cable must be at least that of the shower circuit protection (see Table B).'
Essentially, assuming the issue has been fixed with the replacement and properly wired isolator switch, I would like to know if it's advisable to have the 32A RCBO fitted or just leave the 40A? This assumes 6mm cable left in-situ.
the reference to insulation is regarding thermal insulation, such as glass fibre, rockwool etc stopping the cable being cooled as it warms by the heavy current.Although I'd need to check, I am doubtful any form of cable insulation has been used.
This might surprise you, however we don't all want to learn about the subjects we post stuff on. Sometimes, believe it or not, folk are simply looking for an answer to their question.I actually think he would learn, and remember, more if he worked out the consumption of the shower himself.
do you agree re dropping to 32A RCBO?
Well yes but thats not the case here as its 6mm cablewith a 40 amp MCB/RCBO on a 32 amp rated cable, the cable may overheat.
I was not quoting size of cable, as no idea of the worst installation method for the cable.Well yes but thats not the case here as its 6mm cable
Fair dinkumI was not quoting size of cable, as no idea of the worst installation method for the cable.
The MCB/RCBO is there in the main to protect the cable, and the cable takes time to warm up, as does the MCB/RCBO, but we look at the worst case scenario, so the phone rings, someone steps out of the shower to answer it, and the news need fast action, so the running shower is the last thing they are thinking about, so shower is left running.